icynene under radiant floor
Mr. Blonde
Member Posts: 38
a post on icynene sprayed or poured under a radiant slab instead of 2" high density foam. Has anyone done this or heard of it?
0
Comments
-
Not practical
Foam is sprayed on the walls, not under the slab. R10 blue or pink board is used.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Icynene would be possable sprayed from below under a staple up radiant system but it is way to soft for under a slab. It's also open cell so it would hold moisture under a slab.0 -
Nope...
Icynene does not have the compressive strength, AFIAK. You'll have to look at XPS, a.k.a. Dowfoam, I think. That stuff is tough and won't hold water the way that Polyurethanes (open- or closed-cell) will.
The only application I seem to recall of polyurethanes in contact with soil was the Canadian floor insulation study that featured polyurethane en-cased in metal containers. That's the famous study that exposed the actual efficiency of foil-coated bubble-wrap when used in foundation applications.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements