checkvalves
hr
Member Posts: 6,106
should have info showing the Cv of the valves. The Cv is the GPMs the valve will flow with a 1 psi drop.
Most often using a check the same size of the pipe is over sized. You should select the check by it's flow rate for noise free installations.
I like the soft seat, low pop pressure checks. Conbraco, Watts, and most other valve manufactures offer this type. And a cone shaped check is better than a flat disc type for hydronic applications.
This is a check from the Grundfos Super Brute circulator. Cone shaped, light spring pressure.
hot rod
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=144&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
Most often using a check the same size of the pipe is over sized. You should select the check by it's flow rate for noise free installations.
I like the soft seat, low pop pressure checks. Conbraco, Watts, and most other valve manufactures offer this type. And a cone shaped check is better than a flat disc type for hydronic applications.
This is a check from the Grundfos Super Brute circulator. Cone shaped, light spring pressure.
hot rod
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=144&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
checkvalves
Is there any difference in pressure drop or other performance variables between standard swing checks, "Y" pattern and ring checks? thanks ahead of time.0 -
It takes very little pressure to open a center spring silent check valve. And they work in ALL positions.
TJust a guy running some pipes.0
This discussion has been closed.
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 59 Pipe Deterioration
- 921 Plumbing
- 6.1K Radiant Heating
- 374 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 40 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements