Danfoss valve selection

Steve D_7
Steve D_7 Member Posts: 10
Try this:

It's tough to get US applicable info on these parts.

Use the code number like 013G... to spec your part. Buy the valve and operator separately.

Steve

Comments

  • Keith_11
    Keith_11 Member Posts: 25
    Danfoss valve selection

    I have a client who'd like a Danfoss thermostatically controlled radiator valve installed on a very, very large cast iron radiator. . . just checked out the product literature on their website and am dismayed to find it a mess of stuff. I simply need a 3/4" angled valve with a remote thermostat attached by 6' filament. What control number should I be asking my supplier for? I know that this is a question for the supply house guys, but sometimes it's nice to get the information from the horses mouth. . .
    Thanks,
    Keith

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    Provided that the supply pipe comes up from the floor and angles over to the radiator, and you want the operator horizontal with the floor (standard) you need:

    013G8018 ¾" NPT Side Mount Angle Valve Body

    013G8202 Remote READING (6' capillary tube) Operator

    The ¾" side-mount angle valve (at maintenance ±2° temp regulation) is good for about 2¼ gpm @ 4 psi pressure drop across the valve. This is VERY near the edge of maximum allowable maintenance flow for quiet operation. At a 30° temperature drop across the radiator, that equates to about 33mbh of output from the radiator. If you're close to that requirement, I'd sincerely suggest using a 1" valve body, part # 013G8023

    Fully open, maximum flow is about double the maintenance flow but such a high degree of opening should NEVER be used to maintain temperature as there will be noise and excessive wear.



  • Is this

    a steam or hot-water system?
  • bb
    bb Member Posts: 99
    spot on

    Mike:

    Are you working for Danfoss? You seem to know just as much as the insiders...

    thanks for helping out!

    bb