WM Ultra check valve?

hr
hr Member Posts: 6,106
that is shipped with those Ultras, I installl the circs with the B&G Check-trol iso flange. Be sure to have a Y strainer somewhere in the system. Little copper or solder chips will stick in those checks.

If I pipe an indirect tank I use both the top and bottom connections on the Ultra. I install both circs pumping in to the return side of the boiler. I use the Weil indirects which have very low pressure drop. Pump away from the tank and into the return of the boiler, for the same reason the boiler pump pumps into the boiler.

This assures the boiler sees the increased pressure from the circs to help prevent any flashing in the HX where the intense fire meets the wall of the HX.

Some brands of small condensors have pressure switches on the HX also. If you pump away from the boiler you may drop these out and have lockout issues.

hot rod