Utica PEG 187 steam boiler near boiler piping
ScottMP
Member Posts: 5,884
Frank is that acopper return I see !
Being the Steamheadthat you are, do you see no problem with copper returns ?
I have teased Ron about this, but, if you are onboard also, I may have to rethink this issuie ?
Also I noticed you have a full size equaliser, and not reduced as is the norm. Any comment ?
Scott
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=237&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
Scott
UTICA PEG 187 near boiler piping
What is the correct near boiler piping on a Utica PEG 187 steam boiler. The boiler is rated at 472 sq ft. steam.
My neighbor's boiler is connected using a single 2" taping. Using Dan's book, I did some steam velocity calculations and it seems to me that the steam velocity with just a 2" riser and header is much too high at 34 ft/second. I am thinking that a lot of water is being pushed into the mains and that this is caused hammering and water spurting out of some vents.
Anyway, I don't have a PEG 187 manual handy and I would like to know the correct near boiler piping.0 -
how many.......
sections is it? Is there and equalizer? Is the dimension A 24" or more,(waterline to horizontal pipe/main)? Is the water in the sight glass dirty? Pictures possible?kpc0 -
That's the same
as the Columbia CEG-187. Here's the diagram. It does call for two risers to the header.
The second pic is one we installed. We used a front-to-back header instead of a side-to-side one, but it does the job as well.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Consulting0 -
God bless ya Steamhead
This is the second boiler I looked at on my block where at least part of the homeowner's problem is that there is one riser instead of the recommended two. One is a Utica PEG 187 and the other is a Peerless 61-06.0