main venting on 2 pipe system,more or less important?
Options
Hollis
Member Posts: 105
or maybe the same importance? i have a few one pipe systems and I believe I have enough veting with the big Gorton's but now have aquired a large house that is a 2 pipe with just the smaller Goron's one on each of the 2 lines. After running for a long time I notice that one leg hisses for quite a while so i'm guessing I need more. No room for the larger Gorton's so I will have to antler it. Not sure how many will be work be correct. Can one put on too much/many?
Also I understand the need on a one pipe system but does it apply the same on a 2 pipe system?
Also I understand the need on a one pipe system but does it apply the same on a 2 pipe system?
0
Comments
-
The air has to leave before the steam can enter so venting is important on all steam systems.
What pressure is the system working at, for a two pipe system it should be very low (8-12 oz) and a vaporstat would be a lot better than a pressuretrol.
You cannot have too much main venting, if you want the system to fill with steam at low pressure you need a lot of venting. If venting is not adequate you will pay the fuel company many times more than the cost of the vents in the years to come.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Agreed. And don't forget the dry returns- they need good venting too.
How long are the steam mains and what pipe size?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 424 Carbon Monoxide Awareness
- 72 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 848 Plumbing
- 5.8K Radiant Heating
- 372 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 48 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements