need help reading the pressure gauge
Elena08904
Member Posts: 8
I don't know how to read the pressure. I've attached a picture of the gauge on the boiler. The boiler was not on when I took the picture. Is this okay? Do I need to lower it? If so, how do I know how much?
some background - I just got finished reading Dan's book, We Got Steam Heat. My family moved into a 90 year home in central NJ with steam heat in October. We replaced the 20+ year old boiler within days of moving in. We have radiators that leak LOTS of water, banging noises, etc. After reading the book, I opened all the supply values (I thought they regulated heat so I turned some halfway, now I know that was wrong) and measured my pipes in the basement so I can buy insulation. The one thing I need help with is reading the pressure gauge so I'm posting here. I'm hoping we are on our way to a quieter house with fewer water puddles.
Pressure
Set the right side scale at 2psi. Your boiler should operate correctly at much less than that, but it's the lowest that control allows.
Do youhave more picturesof the boiler and piping?0 -
more pictures
Hi, Thanks for the quick reply. I've added more pictures. One is the boiler. One is taken from the front and the other photo from the side.
Also, most importantly, how do I lower the pressure? Is this something I can do myself?0 -
more pictures
Pressure
There is a slottedscrew on top that can be turnedto adjust it.
That boiler is not piped anything near to correct. That is most definitely causing a lot of your problems.
http://www.usboiler.net/products/boilers/independence/assets/INPV.pdf
Refer to page 7 of the installation instructions.0 -
Elena the photo you have
Is the pressuretrol not the gauge. Adjust the pressuretrol down to its lowest setting to start with. As for the piping it is not as it should be for the system to work properly. The other issue could also be the boiler is not sized properly, I would guess it is too large but that is just a guess at this point.Cost is what you spend , value is what you get.
cell # 413-841-6726
oh boy
Ugh...I had a local (older) plumber who said he had lots of experience with steam heat size and install the new boiler. He has done other work for me so I thought it was wise for me to hire him.0 -
Boiler
Edit0 -
Stictly Steam
Hello Elena,
15I'm a steam homeowner like yourself who has been helped immensely by this site. I might suggest you repost this to the Strictly Steam section and read some of the recent posts. By measuring the edr of your radiators you can see whether or not your boiler is sized correctly. I can't comment on the mistakes made in the piping, but it should be done in black pipe, not copper. This can lead to all sorts of problems.
What kind of boiler do you have? You can probably find the near boiler piping manual online with which to compare your own. What yo are ecperiencing is not normal, but the result for the install more than likely. Good luck.Two-pipe Trane vaporvacuum system; 1466 edr
It has to be piped in threaded steel
I agree the pressure should be turned down to 2 PSI on the main setting, higher pressure just causes problems and you have enough without adding that to the list.
If you look in the install manual that came with the boiler (Burnham IN series?), page 17 is the piping layout for the Burnham IN series. The boiler has to be piped like the diagram or it will never work correctly. Also it has to be piped in threaded steel pipe for the steam because the piping has to move as it heats and cools or it will tear the boiler apart and probably cause the soldered joints in the copper pipe to start leaking.
Call the installer back and tell him the boiler has to be piped per the install manual and it must be in threaded steel on the steam piping, copper is fine on the return side. The system will never work correctly piped like that and the boiler will fail prematurely.
3PSI gauge0 -
piping
I agree with Bob should be repiped in blk pipe with cast iron fittings to allow pipe movement ( see swing joints ) the way it is now there will be pressure against the boiler sections causing problemsThere was an error rendering this rich post.
piping diagrams
Are nice and clear - but I see no requirement for black iron pipe? Methinks they doth assume too much with regard to installer cluefulness...0 -
Steam
I made an appointment to look at her system next week. I'll report more details afterwards.0 -
The problem is
Your boiler is installed sideways.0 -
Update
We fixed the piping and upgraded the main venting. We also went back a few weeks later to thoroughly clean the boiler (wild sight glass movement). Copper always seems to trash up a boiler.
More photos here...
http://www.facebook.com/media/set/?set=a.433213893414525.96184.353747484694500&type=10 -
beautiful work
but how DID you get that boiler to work on its side?0 -
Sideways
It's a dead men secret.0
- 85.7K THE MAIN WALL
- 49 Biomass
- 71 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 38 Industry Classes
- 15 Recall Announcements