Biasi boiler review?
Ragu_5
Member Posts: 315
Have about 30 out there since they replaced the Vega around 2001. All oil and all with Riellos. No leakers and no problems.
Once again, they are a decent, low-cost, 3 pass, low mass cast iron boiler; however, as with ALL low mass units, the big complaint is that they will bounce off of high limit. It's the nature of the beast, and you get what you pay for.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=428&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
Once again, they are a decent, low-cost, 3 pass, low mass cast iron boiler; however, as with ALL low mass units, the big complaint is that they will bounce off of high limit. It's the nature of the beast, and you get what you pay for.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=428&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
BIASI BOILERS-ANYONE HAVE EXPERIENCE
0 -
Do a search
on this site for "biasi" and you will find much previous discussion on these boilers. I have 2 of them in my building.0 -
Biasi
I like them!To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
very good boilers we have installed alot of them but the gas gun makes alot more noise then i think it should
0 -
Biasi boilers
I have installed only one... I liked the why it ran. The only thing I don't care for are the hinges for the front door, if they are not lubed up during maintenace (espicially if you live next to the ocean as we do) I think there might be some issues in the pins breaking...
What are the results of the hinges Mike?
The Kid0 -
Yes
Have installed dozens,zero problems.Very tough to beat for the price. I like them so much I got this plate!
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
I have installed 6 so far. The oldest one has been in place for 2 years. Never had a problem0 -
BIASI BOILERS NJ AND PA.
BIASI BOILERS HAVE A FOLLOWING IN NEW ENGLAND AND IT SEEMS A GOOD FOLLOWING IN NEW YORK. WE RECENTLY BROUGHT THEM INTO PA AND NJ TO DISTRIBUTE. IF ANYONE WANTS INFO CONTACT ME OR TOMANTONELLI.COM0 -
Ragu,
What does 'Bounce off of the high limit' mean?
Thank you,
HE0 -
I think he means
a low mass boiler like the Biasi only has 5-8 gal of water in the HX. Since you can't modulate the oil burner, it quickly hits high limit. I would think a reverse indirect or buffer tank would solve that problem. I'd always pick a low mass boiler with a buffer over a lager mass boiler.
Easier/lighter/more compact makes installation easier and there will be less stand by loss from an insulated tank rather then a boiler with a flue pipe.0 -
Ditto,
"bounce off the hi-limit". What does that mean? MAYBE, just MAYBE, you're not PIPING them RIGHT. Differential is 5-30°F. What do you set it at? But, then again, they're not "V's"; Maybe you got confused with "V'S" way, and "B's" way. But, then everyone "Downeast" might not appreciate, or have the $$'s for your "V" methods, that is, IF, you can get them.
Never had a problem! Maybe you're confusing the pocket books of you're clients, and the proper piping methods of the FINE Biasi, B10 Series, boilers; which have been sold around here (Yes, at one time as G-series Vega's, but essentially the same FINE boiler), for close to 15 years, with the Super-Rich client expectations. The SG series Biasi can be set up to perform every bit as well as a V, for a fraction of the cost. Oil fired "V's" are a hunk of iron just like the "B's". What you do with it is up to you.
Jed0 -
Biasi is not living up to expectations
Purchased a Biasi Riva until in 2008. Since then, I have had numerous issues with this unit. The most recent being that the circuit board has gone bad after only 5 years in service. It's cost almost 30% of the original cost for installation to get it repaired. The warranty is 2 years on all other components and 10 years on the heat exchanger. My Biasi experience has been one that will not allow me to deal with this unit in the future. Buyers beware.0 -
We are talking....
two different units here.... The original posters were talking about the B series oil fired boilers. DIY is talking about a gas fired wall unit. What type of issues? Is this a new boiler in a New system or a boiler replacement in an existing system? What type of issues? Do you have pix? Proper installation is a must w/ the new wall hung boilers. Any electrical board could get fried by a electrical surge....0 -
Just love it....
when people bomb throw here and then never respond to other willing to help fix a problem...0 -
My unit (B 10) is just a few years old and continues to cycle on and off every few seconds. The installers are having trouble identifying the issue. Any thoughts?0
-
Describe your system....
Burner? Zone valves? Circulators? Controls?
Pictures are very good....0 -
Love mine, installed 2 years ago with a Riello burner and it's run without issues. Much more efficient than the old unit it replaced.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 59 Pipe Deterioration
- 855 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements