Third steam boiler in 18 years

NormanC
NormanC Member Posts: 12
edited December 2016 in Strictly Steam





My Burnham Independence steam boiler has just corroded through after 4 years in service. I replaced two Peerless boilers prior that lasted 8 and 6 years each. When I purchased the Burnham I stated to the heating/plumbing company that this cannot happen again and they assured be that Burnham boilers rarely fail. I asked them to look into any problems I might have and all they did is replace a steam trap and fixed the slope on the main line. I had to call them back to skim the boiler the following day because the boiler was surging due to the tap oil in the system.

Clearly I have a problem but no one knows what it is. I have a 1-pipe system with 8 radiators, northwest of Boston, town water.

I keep all the steam vents clean and new. I add about a gallon every 2-3 weeks in Jan-Feb when the boiler is cold. I flush the cutoff valve frequently removing about a quart of water and fire the boiler up immediately to remove the oxygen. The rusty sludge is removed when I see it in the glass.

Thought? I cannot continue to replace boilers at $6000 each every few years.

«1

Comments

  • SWEI
    SWEI Member Posts: 7,356
    What are the pH and chloride levels of your water?
  • Danny Scully
    Danny Scully Member Posts: 1,437
    Has the water quality ever been tested?
  • NormanC
    NormanC Member Posts: 12
    No, the water quality has not been tested. Here is the town water quality report: http://www.chelmsfordwater.com/Pages/ChelmsfordWater_WebDocs/S00609953-04FB1C5E.8/CCR 2014.pdf
  • Danny Scully
    Danny Scully Member Posts: 1,437
    I would start by sampling your specific water and test it's quality.
    MasterBummer
  • SWEI
    SWEI Member Posts: 7,356
    173 PPM of chlorides would generally dictate the use of 316 stainless piping (304SS is good up to about 100 PPM.)

    A demineralizing cartridge may be in your future.
    NormanCMilanDLarry_52
  • NormanC
    NormanC Member Posts: 12
    Should I sample the water from the boiler or from the tap. What's considered bad for pH and chloride levels?
  • Danny Scully
    Danny Scully Member Posts: 1,437
    Is it fed with hot water or cold?
  • SWEI
    SWEI Member Posts: 7,356
    Are you on town water or a well?
  • NormanC
    NormanC Member Posts: 12
    Town water. Manually fed with cold water.
  • Danny Scully
    Danny Scully Member Posts: 1,437
    Test the water out of a cold tap.
    NormanC
  • EzzyT
    EzzyT Member Posts: 1,338
    Does your system have any leaks? Combination of a lot of fresh water make up and poor quality of water will rot out a steam boiler fairly quickly
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
    Paul S_3RomanGK_26986764589
  • Deja Vu.

    I am in touch with heatman to monitor his water consumption, but he is currently traveling and the info is unavailable for another week or so.

    I do have to believe it is excess water consumption or copper/faulty installation until proven otherwise. Do we have a counter/feeder installed to monitor water consumption?

    What is interesting here is that all reports of these premature failures have always been for Burnham boilers, so we have always held Burnham as the culprit. But you state you had two Peerless boilers go early as well, which is interesting.

    Burnham blames it on the chlorides or copper piping. Their solution is to install a MegaSteam boiler. I concur to a degree.

    Send some boiler pics and it's piping please.

    Here is a discussion from 10 years ago from Glenn Stanton (now passed, rest his soul) of Burnham:

    The following is a copy of a post I placed on OilTechTalk to an individual that has had more than of his share of internal corrosion issues where he is located in the South Shore area of Massachusetts.

    Regarding all of the exchanges that we have had over the past couple of years, I would like to clarify the results. As discussed in the past, you have had more than your share of V7 and V8 steam leakers due to internal corrosion. As also discussed, we have paid VERY close attention to this occuring out in the field and have taken several steps to find out why. We have taken water samples from several of the jobsites where this has occured as well as a real close look at the possible contributory things that the system itself can cause. I have discussed most of these things here and at other sites.

    As discussed in previous posts, yes things like uninsulated mains, lack of venting and unattended excessive water makeup can kill steam boilers rather quickly regardless of the brand. One of the primary reasons you folks in your part of Mass. see this happening more often also has to due with the fact that Burnham Steam boilers were installed with greater frequency than other areas so just by percentages you will be seeing more failures. As I stated in all of the previous posts, we have not been resting on our laurels waiting for this problem to go away. We have been exploring the whys of this by sending engineers to your area and to a handful of other areas where this happened with greater frequency than anywhere else. We also brought several of these boilers back and sent them out to independent laboratories for analysis (a very expensive procedure I must add). Most of the people that monitor these sites can support me in saying that they may not see this happening in their geographical areas.

    With that in mind, we concentrated on what may be different about your geographical area than other areas where it does not happen. The one common denominator happens to be the water. It was not so much the water itself but what is in the water which ended up being higher than normal chloride levels. This is also something that we have been closely monitoring regarding stainless steel Indirect Heaters failing sooner than desired. With the indirects we began providing glass lined tanks to use where clhoride levels are high. With the steam boilers the answer is now MegaSteam.

    What we did find is that in areas with higher than normal chloride levels a process was occuring within the steam dome of the boiler called "Temperature Induced Chloride Activated Graphitic Corrosion". This reaction is something that begins with high chlorides in the water and is accelerated by heat or contact of the vertical and upper horizontal surfaces in the steam dome with the flue gasses. It is the contact with the flue gasses that triggers this process and once the ball gets rolling you just can't stop it. Yes it happens with other brands of steam boilers as well but possibly less often for reasons I will explain.

    Now you ask, what is going to make the MegaSteam different than any other boiler out there currently being used for steam? The difference is the flue gas passageway design. This is a horizontal passageway three pass boiler where all contact with flue gasses is below the steam surfaces. There is absolutely no flue gas contact with the cast iron surfaces that have steam on the other side. If you take away the HEAT you no longer have "Heat Induced Chloride Activated Graphitic Corrosion".

    You also ask why this is not happening to some of the older boilers that have been out there for years and years as well as other brands of similar vertical pinned flue design. As far as the newer ones go, they are also susceptible but due to variances in exposed surfaces, pin location and iron thickness it just takes longer. They are all prone due to flue gasses being on the other side of the section walls and dome. As far as the older boilers are concerned, the wall thicknesses were much greater and the exchange of flue gas temperature was not as pronouced due to wider passageways and ribbed surfaces instead of pinned surfaces. In otherwords they just were not as darn efficient. Most of the flue gas temperature was simply going up the chimney.

    We also took a close look at the design of some of the much, much older boilers thant have been out there operating on steam for say 50 to 100 years. Many of these had a common denominator as well. That common denominator is the rear outlet for flue gasses below the water level. They were of either 2-pass or 3-pass design, not very efficient due to the area of the passageways, but none the less below the water line. With all of this in mind we are now glad to introduce the MegaSteam boiler. It is the most efficient steam boiler out there and with protection from the Chloride Activated Corrosion by design....three pass flue gas flow. The testing we have done with this has shown no signs whatsoever of the trigger that starts the chloride corrosion process rolling......heat. That's why we are also the first company to step up to the plate with a warranty that covers internal corrosion.

    Keep in mind that even with the MegaSteam system issues such as uninsulated mains, lack of venting and unmonitored excessive water makeup still have to be paid attention to. We address this in the I&O manual and even go as far as to show a water meter installed on the makeup water line in the I&O drawings. Sorry for the longer than lengthy post and explanation, but I thought you were entitled to it. Thanks for your continued support Heaterman and others.

    The distributors now have their pricing and related information and several have orders in already. These are in production and some may begin to roll ot as early as this week. They will all be shipped out Knocked Down with an assembled block, cartoned jacket and all other related items all enclosed on the same pallet. All I ask is to be patient as the reaction to this boiler being introduced has been outstanding. You will see them very shortly. For now they will all be equipped with the Beckett AFG with other burner options to follow. Thanks again!


    Glenn Stanton

    Manager of Training

    Burnham Hydronics

    U.S. Boiler Co., Inc.
    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
    SWEIkcoppNormanC
  • Paul S_3
    Paul S_3 Member Posts: 1,274
    edited December 2016
    @EzzyT is correct....since you have to manually feed water to the system ... how often is that @NormanC ? .... i saw a brand new boiler fail in 2 heating seasons from a leaking wet return .... i informed the customer during a maintenance the first year and the second year.... i was actually shocked that it failed that quick.... also ALL boilers fail if theres a problem.... use the "find a contractor " feature on this site.....im not sure if @Charlie from wmass would take the trip out to you.... he knows his steam heating.... also you said they replaced a trap? And you have a one pipe steam system? And YOU had to call them back to skim the boiler....they may of overlooked a few things.... also i replaced my aunts steam boiler about 4 years ago and only a total of 6 gallons of water has been added since then....i know because im the only one to touch the boiler
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
    NormanC
  • SWEI
    SWEI Member Posts: 7,356
    Paul S said:

    i saw a brand new boiler fail in 2 heating seasons from a leaking wet return .... i informed the customer during a maintenance the first year and the second year.... i was actually shocked that it failed that quick

    Two words: Water Quality.

    Hard is bad, but corrosive is truly evil.
  • Paul48
    Paul48 Member Posts: 4,469
    "This reaction is something that begins with high chlorides in the water and is accelerated by heat or contact of the vertical and upper horizontal surfaces in the steam dome with the flue gasses. It is the contact with the flue gasses that triggers this process and once the ball gets rolling you just can't stop it".

    Is it just me, or does anyone else see a problem with this statement?
  • kcopp
    kcopp Member Posts: 4,462
    I do know that North Andover has had chloride levels well above average. That will eat through water heaters and boilers.
    I do think you are looking at a filtration system that will deionize the fill water.
  • NormanC
    NormanC Member Posts: 12
    I Just added pics of the pipes and the corrosion near the flue pipe.

    I manually feed the boiler every 2-3 weeks in Jan-Feb. Far less often in the fall/spring. Last week it was low and now I feed it every day. There are no leaks in the system and no spitting vents. There is one copper pipe going to 2 radiators, the remainder is iron.

    It is a 1-pipe system. After I called about the hammering pipes they fixed the main slope (they pitched it wrong after the install) and replaced the trap. When that didn't do the trick I discovered the skimming issue on my own. They said they'd include this step in the checklist for steam boiler installs. This is after they told me they do steam installs all the time.

  • BobC
    BobC Member Posts: 5,496
    Weil McClain claims anything over 200 PPM chlorides is cause for concern. At 175 you are close but not over their warning levels, I assume that level would apply to any low pressure steam boiler but I could be wrong.

    How much water gets added to the boiler every month? Added water brings in oxygen and oxygen can kill a boiler. If you have an automatic water feeder that does not have a water meter on it I would valve it off and add water manually so you know how much water is being added.

    Anytime fresh water is added to a boiler it should be brought up to steam so any oxygen in the water can be driven off.

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
    NormanC
  • NormanC
    NormanC Member Posts: 12
    Not sure exactly how much water is added each month. It's usually a full ball-valve @ 1/2 inch line for about 5 seconds. I always start the boiler after the fill because I have let the boiler (and house) cool off.

    If chlorides are a such a large concern, wouldn't the installer look into this after I told them I replaced 2 Peerless boilers in 14 years before the Burnham? They are from the same town that I am from and should be aware of the water quality.
  • BobC
    BobC Member Posts: 5,496
    If you only open that valve once a month I would not think excess fresh water was your problem. i would find a place to get the water tested just to be sure.

    Do you have anything stored near the boiler (rock salt, fertilizer, open containers of detergent or bleach) that could be getting into the combustion chamber air?

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
    kcoppMilanD
  • At the very least, your need a new contractor. You have a counterflow system and the vents should be out at the very ends of the mains:





    We never want to put a tee at the end of the header either:





    And the equalizer is piped wrong per Burnham. It should head straight down until below the waterline:





    If @Charlie from wmass can't help you, maybe we can.
    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
    MilanDNormanCIronman
  • NormanC
    NormanC Member Posts: 12
    Thank you all for the helpful advice.
  • ChrisJ
    ChrisJ Member Posts: 16,240
    Paul48 said:

    "This reaction is something that begins with high chlorides in the water and is accelerated by heat or contact of the vertical and upper horizontal surfaces in the steam dome with the flue gasses. It is the contact with the flue gasses that triggers this process and once the ball gets rolling you just can't stop it".

    Is it just me, or does anyone else see a problem with this statement?

    Doesn't make any sense.
    I certainly hope the flue gasses never make contact with my steam........
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • This mixing of flue gases is what the 3 pass design of the MegaSteam precludes, for what it's worth.
    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
  • ChrisJ
    ChrisJ Member Posts: 16,240

    This mixing of flue gases is what the 3 pass design of the MegaSteam precludes, for what it's worth.

    Can you kindly explain how flue gasses mix with the steam?
    I think @Paul48 and my self are not understanding what is meant here.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Chris_L
    Chris_L Member Posts: 336
    ChrisJ said:

    Paul48 said:

    "This reaction is something that begins with high chlorides in the water and is accelerated by heat or contact of the vertical and upper horizontal surfaces in the steam dome with the flue gasses. It is the contact with the flue gasses that triggers this process and once the ball gets rolling you just can't stop it".

    Is it just me, or does anyone else see a problem with this statement?

    Doesn't make any sense.
    I certainly hope the flue gasses never make contact with my steam........
    I think this may be a matter of unclear writing. I believe the writer means the outside surfaces of the steam dome normally contacts the flue gases, not the steam itself.

    By contrast, in the Megasteam boiler, he says: "There is absolutely no flue gas contact with the cast iron surfaces that have steam on the other side." Apparently because all of the contact is below the waterline.

    The effect of this would be that the casting above the waterline in an normal boiler would get hotter because it is exposed to the flue gas (on its exterior).
    ChrisJ
  • NormanC
    NormanC Member Posts: 12
    Update: Burnham will replace the boiler for a "small processing fee". However, the contractor is charging $2500+ for a simple rip and replace job. They will not be changing any piping nor will they be investigating the cause of the failure. Can any contractor replace a failed boiler under warranty or does it have to be the original installer?

    If nothing changes I have a feeling I'll be in the same place 4 years from now when the new boiler corrodes.
  • KC_Jones
    KC_Jones Member Posts: 5,805
    NormanC said:

    Update: Burnham will replace the boiler for a "small processing fee". However, the contractor is charging $2500+ for a simple rip and replace job. They will not be changing any piping nor will they be investigating the cause of the failure. Can any contractor replace a failed boiler under warranty or does it have to be the original installer?

    If nothing changes I have a feeling I'll be in the same place 4 years from now when the new boiler corrodes.

    We don't discuss pricing on this site.

    Judging from your pics, that's because they haven't a clue what they are doing. This shouldn't be a simple rip and replace. It's piped incorrectly and all the piping should be pulled out back to the mains and redone.

    Where are you located? We may be able to recommend a good steam contractor in your area.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • EzzyT
    EzzyT Member Posts: 1,338
    Any contractor can replace the boiler via the warranty. As others have stated the near boiler piping needs to addressed and investigate why the boilers are failing so often.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • j a_2
    j a_2 Member Posts: 1,801
    It's great the manufacture is standing behind there product,,,they know the issues involved....As spoken that boiler may be a steam boiler but it's not piped like a steam boiler...Whoever did it and whoever proposes a simple swap out, dump them all.....Get 2 proposals and post them, less names and pricing...of course....I will as others here will watch out for you.... You need to think with your head and not your wallet...not saying you did not due that....Trust no one till you do your research
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,472
    The guys are right, dump the boneheads! They shouldn't give you ANY problems have a qualified, licensed heating contractor do the new install. I really INSIST you try and get one of the FIND A PROS from here. They will do it right. Mad Dog
  • gerry gill
    gerry gill Member Posts: 3,078
    Why not have a tank with a transfer pump that has 'perfect' boiler water from say Rhomar or somebody, in it to use with the boiler. After all, how many or should i say, how few gallons a season of water are you actually using.
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

    j a_2
  • j a_2
    j a_2 Member Posts: 1,801

    Why not have a tank with a transfer pump that has 'perfect' boiler water from say Rhomar or somebody, in it to use with the boiler. After all, how many or should i say, how few gallons a season of water are you actually using.

    I think in his case that is exactly the correct way to go....Great thinking on your part...Hopefully he gets his system tightend up
  • gerry gill
    gerry gill Member Posts: 3,078
    Maybe with this stuff instead of water.
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

    SWEI
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,296
    I would get Burnham's approval to use that fluid just to be safe, I am sure they would be fine with it.

    I would still get the water analyzed as others have mentioned.

    And the piping may be not the best but that didn't cause the boiler to fail.
    LionA29
  • NormanC
    NormanC Member Posts: 12
    Apologies for discussing price on this forum.

    Thanks for the advice guys, I'll find installer from this site near eastern Massachusetts.

    Happy Holidays.
  • I think bad piping could cause an early boiler failure. If the water is blown out of the boiler, enough to trip the LWCO and cut the burner, then there would be a degree of thermal shock, which over time and many cycles would open up minute cracks in the castings. The returning water will be slightly cooler, and put the 215 degree metal under a sudden stress.--NBC
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,296
    I didn't say improper piping couldn't ruin a boiler. My conclusion was based on the pictures that I don't think improper piping killed this boiler
  • Larry_52
    Larry_52 Member Posts: 182
    I would like to point out that the incoming water supply at 173 ppm chloride content is relatively harmless for LP steam boilers by itself. What does cause concern is cycle concentration. If you leak primarily leak steam in your system and add water to makeup you are compounding the chloride level (cycle of concentration). Chlorides do not travel with the steam and stay in the boiler. Can you test incoming water for the ORP, LSI index, its pH and hardness? I want to know how much of the chloride content is attributed to sodium versus Mg and Ca. I also am more curious what the oxidation redox potential (ORP) of your water is because they need to use an oxidizer to regenerate those greensand filters they are using.