3/8" steam return (?)
bluemoon
Member Posts: 41
I'm hoping someone can tell me how this works (it seems to). I was inspecting a heating system for a prospective home buyer & found the 1st floor freestanding radiators had been replaced with 1-1/4" baseboard supplied by the old radiator riser on one end with a Hoffman #500(?) vent teed on the opposite end....the bottom of the tee is reduced to 3/8" copper & extends down into a tapping on the steam MAIN. The 3/8" has a trap (loop) in it by design. I turned on the heat & from a cold start the baseboard heated . Is this some method of installing baseboard to steam that anyone has seen elsewhere?...it's a first for me but it seems it was working in the short time I tested it.
0
Comments
-
Not how I would like it, but it is better than nothing to drain the condensate.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Actually, Dan describes this on page 100 of "The Lost Art of Steam Heating". It works!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
I have never used less than 1 /2" for a return.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Gerry has, on his mini-tube system. In this application, all you're handling is a trickle of condensate, so as long as it works properly................All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 117 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 111 Geothermal
- 163 Indoor-Air Quality
- 3.7K Oil Heating
- 72 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements