Puzzler: Condensate Return Leak, LWCO, Auto Feeder
zwiegand
Member Posts: 5
Looking for some thoughts from the wise people
here. We have determined that there is probably a leak in our buried
condensate return piping, and I'm trying to sort out if our float-type
LWCO may also be malfunctioning.
My system: HB Smith 2500L
steam boiler with domestic hot water coil. Runs on a Heat-timer
EPU-CH. McDonnell & Miller 67 float LWCO with McDonnell &
Miller 101-A water feeder. McDonnell & Miller probe LWCO with
automatic reset, just below the bottom level of the sight glass.
Hartford loop an inch or two below the probe LWCO (seems a bit lower
than usual).
Symptoms: Waking in the morning with no heat
or hot water. This only happens when night temperature does not call
for heat and the system is idle through the night. I check the boiler
and there is no water visible in the sight glass, the red light is
blinking on the probe LWCO. I fill the boiler manually by pushing the
button on the water feeder and as soon as the level reaches the probe,
the burner fires up. This takes about 2 or 3 minutes, and after another
2 or 3 minutes the water level is nearly at the "normal" line. After
this the system runs normally as long as the Heat-timer calls for heat
and cycles steam once per hour. I have put the Heat-timer in summer
mode and observed that the water level dropped about 2" over a 2 hour
period.
Hypothesis #1: Water is slowly leaking from the
system and the float LWCO is sticking and not signaling the water feeder
to work. Water continues to drain and the probe LWCO eventually shuts
the system down. I like this hypothesis because the system seemed to
produce hot water fine for the summer and our leak is only now being
exposed because the LWCO is malfunctioning and not turning on the water
feeder. The only reason I am in doubt is that everything still runs ok
as long as there is a call for heat. We know there is a leak, so at
some point the float LWCO must be triggering the water feeder. Is it
possible that the flow of water through the return piping during steam
production slows the leak enough to not require makeup water? Or maybe
just the way water is moving through the system prevents the float from
sticking? Also note: when the system is producing heat, opening the
blowdown valve on the float LWCO does actually trigger the water feeder.
Hypothesis
#2: At some point during the night, water leaks quickly from the
system. The float LWCO signals the water feeder to turn on, but it
cannot keep up, and eventually the float LWCO turns everything off,
including the water feeder. Water level continues to drop until the
probe LWCO also activates (Do these LWCOs turn off the water feeder if
the cutoff water level is reached?). I have doubts about this
hypothesis as well because I would think that the float LWCO would need
to be reset by bringing the water level back to near normal before the
system would turn on again. As I said before, the system turns back on
as soon as water reaches the probe LWCO, which is well below the float
LWCO.
Thank you all for reading and I hope you can help me solve this puzzler.
than usual).
period.
Hypothesis
LWCO.
I would start by fixing the leak
And then You can monitor the feeder0 -
re: uzzler: Condensate Return Leak, LWCO, Auto Feeder
I'm just an amateur so take my thoughts with a grain of thought.
I too would guess that the problem is the main LWCO/feeder switch getting stuck and unstuck -- we recently had that happen to us. (ps. A quick fix to that stuck float valve was a hard punch to the LWCO).
We also have a buried return leak that is impractical to fix, which indirectly causes more fresh water and thus rust in the water.
I would suggest a first step of installing a new water feeder that measures the amount of fresh water fed into the system. There is a VXT model that it mentioned on the forum a lot that works fairly well.
That's what we installed and it is absolutely essential to understanding the nature of the water loss. It will let you see how much water you are losing and when.
With that information you can both diagnose how bad your leak is, and when the LWCO is calling for water.
As soon as you conclude that it's unlikely that your system is simply calling for so much water that its purposefully shutting down the boiler, and you conclude that the LWCO float is getting stuck in some fashion, i would replace (or clean?) that LWCO float switch. I get nervous about relying on the backup LWCO so yeah, if in doubt i'd probably replace the LWCO float/feeder sooner rather than later.0 -
Seems to me
that something is slightly amiss with the controls (as well as the leak, patience). In my view, either low water cut off should shut off the system, and it shouldn't run at all until both are happy. The behaviour you describe, where it will turn on when the probe type unit is satisfied, even though the float unit isn't, and the water feeder doesn't activate automatically under those conditions, suggests very strongly that the float unit isn't working properly.
It is possible that the vibration of the boiler firing may be enough to allow the float unit to operate properly and activate the feeder, and that the leak is enough so that at night when the boiler isn't firing the water level drops below both LWCOs (the float unit having hung up) and shuts the system down.
They can be cleaned (you do flush it once a week or two, don't you?) but once they start hanging up it is -- in my humble opinion -- better to replace them. This is a safety device, after all...
Now that leak. 2 inches in 2 hours is wildly excessive. Even if you get things fixed so that the boiler will run, that much fresh water is going to corrode that boiler and give you more, and more expensive, problems. Find it and fix it.Br. Jamie, osb
Replace LWCO, Install Meter
Thanks to those who have commented so far. The consensus seems to
be that the float LWCO is malfunctioning. We are definitely planning to
find and fix our leak, but it will take time because our return pipes
are buried in the basement of a commercial space that we do not own.
Anyway, I think our immediate plan should be to replace the float LWCO
and to install a meter on the feed line. Any thoughts on whether the
meter should be upstream or downstream of the feeder? In our case it
would be much, much simpler to install it on the output side.
Thanks again for the help everyone!0 -
Test to be sure
Test the return.
Any time I suspect a return leak, i perform the following test:
Cut the return loose on each side of the point were it disappears into the floor (Yes, I know, it's a pain bc it's iron piping, so you may have to need to add a cpl of unions and replace back to the next fitting, if you don't have a threader)
Try to do it at roughly the same height on each side.
Fill the return with water and monitor it for bit and see if the water level goes down.
This will confirm a leak beyond any doubt.0 -
Greetings from long ago and not so far away
Has that lobby return leak got worse, or is it difficult to tell?
Maybe it should be on your New Years resolution to do some repiping!
Let's start a new thread on that.--NBC0 -
re: test
Thanks for that testing advice -- that's actually a pretty good idea that could come in handy..0 -
lwco
lwco can be taken apart and cleaned, the sa101 has a strainer that should be cleaned or replaced at least every 6 months, a plugged up lwco could be part of the problem as others have saidThere was an error rendering this rich post.
- 85.7K THE MAIN WALL