On that WM EG30 boiler I'm installing, should I run two 2" risers into a 3" header. Or should I size it to a 2 1/2" header.
DL Mechanical LLC Heating & Cooling 732-266-5386
Specializing in Steam Boiler Replacement, Serving most of NJ
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

https://m.facebook.com/DL-Mechanical-LLC-315309995326627/

I cannot force people to spend money, I can only suggest how to spend it wisely.......
·

Comments

  • Paul SPaul S Posts: 876Member ✭✭✭
    manufacture

    What does the manufacture say?I usually use the size the manufacture states for the risers and I go up a inch for the header...for example of it says 3 inch header I use 4 inch Paul S
    ASM Mechanical Company
    Staten Island NY
    347-692-4777
    [email protected]
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
    ·
  • JStarJStar Posts: 2,668Member ✭✭✭
    Header

    ****Header Size per Maximum BTUH Output****

    (Based on Velocity of 15 ft/sec. to 20 ft/sec.)

    2" Header = 48,384 - 64,512

    2.5" Header = 68,832 - 91,776

    3" Header = 106,416 - 141,888

    4" Header = 183,312 - 244,416

    5" Header = 287,856 - 383,808

    6" Header = 416,016 - 544,688
    - Joe Starosielec
    [email protected]
    ·
  • Dave0176Dave0176 Posts: 446Member ✭✭✭
    Thanks Jstar

    I seen that chart, but I also seen 3&4 section boiler 3" header 5&6 section boilers 4" header??? Should I run at least a 2 1/2 header??
    DL Mechanical LLC Heating & Cooling 732-266-5386
    Specializing in Steam Boiler Replacement, Serving most of NJ
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
    ·
This discussion has been closed.

Welcome

It looks like you're new here. If you want to get involved, click one of these buttons!