tekmar 256
Paul S_3
Member Posts: 1,261
I was called on a job to wire a boiler using a tekmar 256....a different heating contractor installed boiler and could not wire customer provided control...I know how to wire it but when you have to put in what type of radiation is being used what do I put in if there's a combination of baseboard and radiant heating.....?....there is no boiler protection loop for low return water temp...thanks Paul S
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
347-692-4777
ASMHVACNYC.COM
Tekmar curves
From http://tekmarcontrols.com/images/_literature/e0003_06.pdf
There is a minimum target temperature setting for the boiler that sets the bottom of the curve.0 -
256
Paul,
The 256 will control the boiler with outdoor reset. You can set the boiler minimum output.
It is not designed for two temp systems or boiler protection.
Albert Einstein0 -
256
I can still use it right?....do they make a control for 2 temp systems? Thanks paul S (in other words what type of control you wouldve used on a application like this)ASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Two temps
A 363 will manage two separate reset curves. They're somewhat pricey.
I'd probably just add a Taco iSeries-R for the RFH.0 -
tekmar 256
How come this control has a room occupied temp setting and a unnoccupied temp setting if it does not actually sense temp....i believe its a parallel heating curve ...can someone explain that? thanks paul sASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
It's a curve shift
triggered by an external signal.0
- 85.7K THE MAIN WALL
- 49 Biomass
- 71 Chimneys & Flues
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 38 Industry Classes
- 15 Recall Announcements
