HoneyWell 8043G Zone Valve Question

Can I use the 2 red wires on the zone valve ( END SWITCH) as the switch that sends 120 volts to a circulating pump?
·

Comments

  • SWEISWEI Member Posts: 7,025
    edited October 2013
    Rated for it

    End Switch Rating: 50 VA pilot duty @ 24 V; 4.4 A running with 26.4 A inrush @ 120 V



    Edit: didn't think about the code issues mentioned below.
    ·
  • RJRJ Member Posts: 445
    relay

    Use a honeywell R845A 1030 relay package
    RJ
    ·
  • hot rodhot rod Member Posts: 5,712
    via a relay only

    you would not want to put line voltage on the bare, exposed terminal strip connections. The space under the cover is not properly separated to mix low voltage and line voltage, if you tried to wire directly into the ZV.



    A relay box is the correct and safe way to relay the voltage. Honeywell, Taco, Argo are a few common brands.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    The magic is in hydronics, and hydronics is in me
    ·
  • [Deleted User][Deleted User] Member Posts: 23
    bring it to the aquastat if you have the room

    run it to the aquastat or use a relay of some sort.
    ·