What is impact ?

FizzFizz Posts: 211Member
If capacity of air return line is less than connected sq ft of radiation?  Currently have 1" return line with radiation sf  of 234.  According to tech data on system, max for 1" return is 200sf.  System is Richardson.
· ·

Comments

  • SteamheadSteamhead Posts: 8,883Member ✭✭✭
    You'll probably be all right

    the proof is how evenly and well the radiators heat up- any issues there?
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    · ·
  • FizzFizz Posts: 211Member
    Issues, yes.

    Continue to have no heat getting to 2nd floor rad.  The rad had stuck Rich valve, which was replaced with Mepco orificing valve.  The rad is not blocked, the Rich el is clear, riser, and connecting pipes are pitched ok.  Possible prob is the rad is on lateral from main, 3/4" pipe, with 3 other rads run off it also, having a connected load of 90, more than Richardson specs of 80.
    · ·
  • SteamheadSteamhead Posts: 8,883Member ✭✭✭
    Have you cleaned

    the little air hole in the part of the Richardson elbow that sticks into the radiator?
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    · ·
  • FizzFizz Posts: 211Member
    Air hole clean

    Removed el, air hole clean, pipe open, no sludge on bottom of rad.
    · ·
  • BRIANJBRIANJ Posts: 116Member ✭✭
    HAD A SIMILAR ISSUE

    Recently I had a similar issue with my Broomell system. Radiator was not heating so removed valve and had steam, removed return ell and had steam. Figured problem was somewhere in the return. Got out the shop vac and left it on for about 10 minutes then reversed the vac to blow into the return for 10 minutes. Then alternated between Vav and blow about 3 times. Problem solved. Radiator now heats perfectly. I don't know what was blocking the return but everything is working now.  Good Luck, Brian
    · ·
  • FizzFizz Posts: 211Member
    Interesting idea

    Will try it, have nothing to lose.  Thanks Brian.
    · ·
  • FizzFizz Posts: 211Member
    Interesting idea

    Will try it, have nothing to lose.  Thanks Brian.
    · ·
  • FizzFizz Posts: 211Member
    Vacuumed into vacuum

    Used shop vac, initially blow, but duct tape blew open in seam, reversed to vac, and system went into deep vacuum, then reversed to blow, and water flushed out.  Any event, rad still not working, heat gets to near or at valve and stops. 
    · ·
  • Charlie from wmassCharlie from wmass Posts: 2,966Member ✭✭✭
    I just had this with a Broomel

    system I worked on. Turns out the boiler was being fired at 1.1gph and the system required a 3gph fire rate. If you throttle down other  radiators that are heating well does this radiator heat better?
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
    · ·
  • FizzFizz Posts: 211Member
    Robbing Peter to pay Paul?

    The radiator's riser is at end of run-out which has 2 laterals supplying 3 other rads.  The pipe is 3/4", thinking by throttle back less heat to areas where more is desired.  Wondering if re-piping radiator in question directly off main would help?
    · ·
  • ChrisJChrisJ Posts: 2,818Member ✭✭✭
    Stealing

    My system is a simple 1 pipe setup, but if I vent my bedroom radiator too fast my upstairs bathroom (on other side of house, on other steam main) barely gets steam and it gets it later in the cycle.  If I vent the bedroom slower, that bathroom gets mighty hot fast.
    Weil-McLain EG-40 connected to 392sqft of radiation via two 2" risers into a 3" drop header and 2" equalizer. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment Typical operating pressure 0.5 - 1.0 inch wc.

    Steam system pictures updated 1/25/15.
    https://picasaweb.google.com/thetube0a3/Boiler?authkey=Gv1sRgCImUxIqv9436MQ#

    Don't push the envelope, eliminate it.
    · ·
  • FizzFizz Posts: 211Member
    Add-on rad the culprit?

    Throttled-back sevreral rads from each loop with no affect on rad not heating; then shut-off add-on to lateral that feeds off lateral to non-heating rad-let there be heat!  Problem is the add-on is a traditional trapped rad, only 30sf of radiation, yet it's end of lateral to 24sf rad.  Tried feeding less to add-on, but it seems to rob rads in question of heating ability.  Would like to repipe add-on to other 2 add-ons which have there own supply run off main, but don't think it's physicall possible.  Alternative move maybe to pipe non-heating Richardson to other 2 add-on run.
    · ·