Fenwal flame strength
Plumdog_2
Member Posts: 873
What's the correct method of determining flame signal strength with a RCLY type hot surface ignition control? I think it has pins marked F(C) and F(+). Burner drops out 1/2 second after lighting. Newer but generic ignitor. Working OK for awhile, then a bolt of lightning took out phones and computers in this particular mansion. Thanks for your help in advance!
Rob
Rob
Put your meter on microamp scale
and leave the wires connected to the F+ / FC connections, then just place the two leads from your meter right on F+ FC.
I am not sure I am familiar with RCLY type hot surface ignition control. Do you have a picture? Be careful with Generic igniters as they may not match up electrically with some boards.0 -
Tim...
If I am not mistaken, an amperage reading has to be taken in series with the circuit, no?
What I have done in the past, is to connect the positive lead of the DMM to the F+, and the other lead to the terminal on the board for F+, then touch the two together, and allow the systems to start. Once started, put the circuit into a series, by un-touching the two leads, and you should be able to see the flame signal current.
Granted, it has been a while since I've had to do this, but if memory serves me correctly, this was the methodology spelled out in Honeywell's Troubleshooting manual for their universal ignition control module that uses the flame sensing circuit.There was an error rendering this rich post.
Fenwal is different than
everyone else in that they provide two direct terminals for taking microamps with out disconnecting the leads on their modules.
If you are talking about Industrial Flame Safeguard Honeywell Controls (R4795 or the old RA890E) that is a different animal than Honeywell say S8600 modules. On those you simply brake into burner ground wires and put the meter on microamps and and place it in series with the wire coming off the sensor and burner ground. If it is a dual rod pilot system you can use burner ground or the sense wire both give the same reading.
The method Honeywell gave you for the Universal Module was there way of doing it. When I went on board with them doing the Source training in 1994 I showed them that my way was easier than the method they were teaching. They never did however take it out of their manual.
It work for me and it is up to date as I just did readings in class on both a Fenwal Module today and a S8610U-3009 the new Universal module from Honeywell.0 -
I learned something today...
Thanks Tim!
My reasoning for the probe contact/un contact is that when the ignition module is sparking, some of that voltage bleeds back through the sensing circuit and scrambles the brains of the DMM.
METhere was an error rendering this rich post.
Drop-out current for Fenwal ignition module
According to Fenwal, the 35-65 ignition control module should "see" a minimum of 0.7 microamps with a good flame. I am working on a two burner Nortec humidifier that is experiencing intermittent flame failures on the #2 burner. With both burners operating, I am only reading 0.1 to 0.2 microamps at the F+ and F- flame sensor terminals of both controls but the burners continue running. At some point, naturally when no one's around to witness it, the #2 control locks out. I've tried calling Fenwal's tech support but they don't answer their phone or reply to my voicemails. I've swapped the modules but the problem remains with the #2 burner. The flame rods and hot surface ignitors have been replaced numerous times by another contractor. Any advice?
Thanks, Rick0
- 85.7K THE MAIN WALL
- 49 Biomass
- 71 Chimneys & Flues
- 92 Geothermal
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 848 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 50 Water Quality
- 38 Industry Classes
- 15 Recall Announcements
