Hartford Loop?
JohnLaPlante
Member Posts: 49
Hi all,
Please see the attached picture. The diagram on the left is how I see the Hartford Loop pictured in the boiler manual for my boiler (Weil EGH-85-PI). The diagram on the right is how my wet return piping is configured.
I have to have some of this piping replaced this summer, but not all of it. However, I'm seeing a big difference between how my piping is configured and how the boiler manual recommends. It probably wouldn't be a major additional expense to have it all replaced, but I'm wondering what all of you think?
Thanks...appreciate all of your help and feedback!
John
Please see the attached picture. The diagram on the left is how I see the Hartford Loop pictured in the boiler manual for my boiler (Weil EGH-85-PI). The diagram on the right is how my wet return piping is configured.
I have to have some of this piping replaced this summer, but not all of it. However, I'm seeing a big difference between how my piping is configured and how the boiler manual recommends. It probably wouldn't be a major additional expense to have it all replaced, but I'm wondering what all of you think?
Thanks...appreciate all of your help and feedback!
John
0
Comments
-
As I understand it John
Re- the manufacturer drawing. The steam comes out of the boiler like the red arrows. Then it goes through the header which separates(?) the steam from the water. The steam goes up into your house and the water is sent down the equaliser, past the Hartford, and back into the boiler to be re-heated into steam. As the separated water goes past the Hartford it sucks the Hartford water back to the boiler also.
In the second drawing, the steam starts out the same way out of the boiler, but when it gets to where I have drawn the arrows, you have 2 forces trying to go opposite directions. They collide head on. The pressure of the boiler might even push the returning condensate in the wrong direction. If this is indeed what is happening the boiler might get low on water, or the water might get trapped upstairs (wet air vents). To confirm this, while it is running, and don't burn yourself, measure the temperature where the red and blue arrows collide. You may see the steam is going up the wet return and pushes the returning condensate back. Of course, after it shuts off, everything goes back to normal and the water returns to the boiler.
Anyway, this is how I understand it and I may be wrong, or did not explain it right but I thought I would at least try, since you have been waiting for an answer for 20 plus hours.0 -
Aha!!
This makes perfect sense! I posted earlier about a vent overflowing with water...I will bet that the pressure is pushing the water back through the wet return piping and causing it to back up in piping. When we put that vent in, it gave a pathway to push the water all the way up the wet return and out the vent...think so?
Thanks so much for the response...I think I will have all of the Hartford loop piping replaced this summer.
Cheers!0 -
The guys here talked me into doing this type of thing
I do not regret it. My plumber thought I was nuts when I told him I wanted to break up my one main and form two separate loops. Respect for the deadmen and all that. It runs real good like this. It took some time to tweak it but my bills are way down this year.
I just looked back on your wet vent post. I am not sure if this is a good thing for a mouat system.0 -
Had a similar situation
not too long ago . The orientation of the Hartford Loop tee was like yours is now . Inspector failed the job because of it . For the life of me I can't see how it would adversely impact steam operation , as long as it's at the proper height ( usually 2 to 4 inches below the normal water line ) . The system worked fine for a few winter months till we scheduled the repipe .0 -
Thanks!
Ron...thanks...appreciate the post!0 -
Crash...
...thanks...not sure either... Hopefully we can get to the bottom of things this spring/ summer when we have the work done.0 -
Ron it leaves a long horizontal
with very little net pressure or flow to move the debris. It will clog in short order. This is also why the Hartford loop nipple should be close or a wye. In the wye configuration gravity keeps the sludge from clogging the horizontal. Water moves really slow at that elevation and with the tee that way you are asking it to make a hard left with no power.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Charlie - Thanks!
I think this is all related to what I suspect is a clogged wet return pipe along one part of my system. Thanks for the input!!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 418 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 856 Plumbing
- 6.1K Radiant Heating
- 372 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements