Indirect water heater
Dana
Member Posts: 126
You don't.
Heat exchange
When a cold start boiler gets a call from the indirect for heat, how do you keep the heat from going from the indirect back to the boiler, and therefore running out of hot water? I was helping a friend of mine today, and I asked him what he planed on doing. He didnt have an answer. He understood what I was saying, but didnt know how to stop it from happening.
Normally I install a Buderus, with the Logomatic control, or a Munchkin, so I have not run into this issue.
Any ideas would be helpful.
Thanks in advance,
Chuck
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Contractor"0 -
timers/delays
there isnt a timer or a delay, that would allow the boiler to run for a couple of minutes before starting the circulator feeding the indirect?
Chuck
Reverse Aquastat
You can hook up a reverse aquastat "B" to prevent the problem .I believe the 2107 has a setting to prevent the circulators from kicking on below a desired temperature for condensation .0 -
Never really
thought about it, but you're right; the warm water coming back from the indirect would pre-heat the boiler.
The Viessmann Vitogas boilers have a thermostat that disables the pump until the boiler gets to 130° to prevent condensation. That feature could be used for more than one purpose.
But come to think of it, it really doesn't take very long to heat the boiler water; there's only a few gallons in the indirect system.
Chuck, Most cold start boiler I know of have their own recommended control statigy. Some supply and include whats needed, others just recommend something.
EK is a good example of a non-condensing oil fired colds start boiler, and their controls don't open the dhw zone, or any others unless the boiler return temp. is warm enough.
A triple aquastat (double acting aquastat) would work, as they canbe set up so the pump/zone doesn't kick on unless the temp. is above the low setting.
Or as other recommended a normally closed aquastat that opens on temp. rise would work. I'm sure you could also give the dhw priority this way too.
If this is a non-condensating type boiler, it gives you another reason for wanting to do this.
Steve
reverse acting aquastat
Seem like everybody hooked up too all this HI-TECH boola-boola and forget about the OLD L4006B (B)as in boiler).Just set it at 130 deg and Walla.0 -
Amtrol
Amtrol's latest version of the smart control (the one with three buttons instead of just one) has a prepurge setting. the options are 0, 4, and 8 minutes. I believe the manual says that it is useful for cold starts and for larger boilers.
Tom M.0