I think I have an under sized boiler. Is there some simple math a DIY can use to figure the load on the rad's in my house. The boiler I have puts out 450-495 EDR I think it runs to long to get steam to all of my radiators.
Thank You Jim
Thank You Jim
0
Comments
-
Retired and loving it.0
-
You also may have
an air-venting problem. Are there large vents at the ends of your steam mains? What type of system is it- one-pipe, Vapor etc.?
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0