One thermo jumpered to second thermo contact on my switching relay panel?
Options
uhehs
Member, Email Confirmation Posts: 1
Hi. I have an ARGO ARM-4p four zone panel. Right now, each zone and each circulator has its own thermostat. If I want to get rid of one thermostat (taking down the wall altogether), so.......... can I run jumper wires from the Zone 3 thermo connections on the Argo panel, to were Zone 4 thermo connects to the panel, to then operate Zone 3 and Zone 4 simultaneously from one thermostat? Thank you in advance for your help.
0
Comments
-
Sure you can.0
-
-
Don't worry about controlling the temps. That why Burlington Coat Factory sells coats.
The reason was that you had 2 isolated zones, but with the wall gone you will now have one zone operating from 2 ZVs. Keep the thermostat that most accurately records the room temp unless, of course, one is on the wall you remove.0