Does the flow rate through the Hydraulic separator have to be equal to or greater than the maximum flow rate of the boiler? The max flow through the boiler is 13.3 gpm and the 1" separator has a max flow of 11 gpm. Should I get the larger separator with a max flow of 18 gpm?

Thanks

Comments

  • Tinman
    Tinman Member Posts: 2,808
    Options
    I’d be focused on the actual flow rate. What is that?
    Steve Minnich
  • hot_rod
    hot_rod Member Posts: 22,143
    Options
    As @Steve Minnich asked, what is the actual flow rate you will be running? There is some wiggle room in that flow rate, 13 gpm if you in fact run that, should be fine.
    The high flow rate number on the boiler may be at a tight ∆T, which you probably are not trying for?
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream