aquastat L8148E burnham boiler

Options
augie1
augie1 Member Posts: 8
thank you for your time. Question is i have a burnham boiler the sysytem is working BUT i noticed when the thermestat is NOT calling for heat the relay inside the aquastat is IN [energized] and when the thermestat calls for heat the relay in the aquastat DROPS OUT [de energized] and the boiler fires up and works fine..SHOULDN'T be the opposite?? This aquastat was replaced 5 years ago and we had no problems since. again i say the boiler is working fine. thank you .

Comments

  • HVACNUT
    HVACNUT Member Posts: 5,835
    Options
    On the clapper, out is on, in is off.
    If the heat is not on, you can gently pull the clapper and the burner and circulator will start.
    STEVEusaPA
  • augie1
    augie1 Member Posts: 8
    Options
    great , relay out when boiler is fired up , and in when thermestat is not calling for heat [boilre off] THANK YOU SIR.




  • STEVEusaPA
    STEVEusaPA Member Posts: 6,506
    Options
    HVACNUT said:

    On the clapper, out is on, in is off.

    If the heat is not on, you can gently pull the clapper and the burner and circulator will start.

    Clap on...clap off...the clapper!
    steve
  • augie1
    augie1 Member Posts: 8
    Options
    Gotcha thanks AGAIN.
  • augie1
    augie1 Member Posts: 8
    Options
    Gotcha thanks AGAIN