Electicians! Question about fuse substitution

Jamie Hall
Jamie Hall Member Posts: 23,161
I am afflcted with a 70 amp rated Royal Electric Company type XJ-48 fuse. Not to exceed 250 VAC rating. It's old (like about 70 years old). It blew for no known reason (wiring checks out with a megger).

Is there any good reason I can't substitute a Littlefuse Time Delay 70 Amp 250 VAC FLNR series for it? Dimensionally the same.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England

Comments

  • JUGHNE
    JUGHNE Member Posts: 11,042
    edited June 2019
    I can see no problem, maybe even prevent a nuisance opening if there is any motor load involved.

    Is your old fuse the changeable link type?
    Years ago you could buy just the links and the ends of the cartridge would unscrew for changing.
    Not in use any more as there was some replaced with just copper wire for the link, never a blown fuse then.
  • Fred
    Fred Member Posts: 8,542
    JUGHNE said:

    I can see no problem, maybe even prevent a nuisance opening if there is any motor load involved.

    Is your old fuse the changeable link type?
    Years ago you could buy just the links and the ends of the cartridge would unscrew for changing.
    Not in use any more as there was some replaced with just copper wire for the link, never a blown fuse then.

    Just the occasional fire! >:)
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    What is the connected load Jamie? And what is the conductor insulation and type (ie NM cable, BX, open conductor, etc)?
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • Jamie Hall
    Jamie Hall Member Posts: 23,161
    It's a main fuse -- actually two of them (240 volt single phase) -- protecting an underground line to one of the outbuildings. The whole thing was put in in 1955 after hurricane Diane took out the overhead lines, and honestly I'm not sure what the insulation is -- direct burial anyway, three separate conductors. There is a 60 amp two pole main circuit breaker at the other end -- on the building distribution panel. Maximum connected load is around 50 amps/240 volts, mostly heating units but some lighting and "convenience" sockets. There used to be a 3 hp motor in there, but that went some years back.

    I may say, somewhat parenthetically, that this place is an electrician's nightmare... all done to code -- but to the codes in force when various work was done. Interesting...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,452
    Your always safer with time delay fuses. What is your wire size? Is this a motor load?

    On NON MOTOR circuits fuses (in general) are sized for the wire so for a 70 am circuit #4 wire is normal

    On a motor circuit only the old "one time" fuses were sized at up to 300% (3x) the motor running load. Time delay fuses are usually sized at up to 175% (1.75x) the motor load.

    Motor circuit fuses have to handle the starting current which is why motor circuits are allowed to be "overfused" but only when the motor has overload protection either inside the motor, a motor starter or a vfd
  • JUGHNE
    JUGHNE Member Posts: 11,042
    The old 70 amp fuse may have been "punched" by the 3 HP motor that is no longer there. Hit with hard starts enough to weaken the link putting it close to opening.
    Feeder wire should be #4 copper or #2 aluminum.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,452
    60 amp breaker is limited to about 48 amps of load. Most breakers will tip if run at over 80% of rating for any length of time.

    The "three" separate conductors is bothering me a little. 2 hots and a neutral? What are they using for the equipment ground?

    Maybe they are using the neutral for an equipment ground as well which would be illegal nowadays. Don't know if that was legal in the old days. You only see that on older stoves and electric dryers
  • pecmsg
    pecmsg Member Posts: 4,775
    The way that he would determine whether or not it's really all right would be to use a Cooper bussmann cross reference that would tell him if those fuses are permissible. I would have to think that they are, since most of the fuses we use in hvacr are indeed time-delay fuses...so he could double check with Cooper bussmann but I wouldn't have any compunction about using that fuse, as long as it's dimensionally the same and has the same over current capacity.
  • JUGHNE
    JUGHNE Member Posts: 11,042
    edited June 2019
    IIRC, an install this old would have allowed a 3 wire service to an outbuilding. The neutral would have been bonded to the sub feed panel with a ground rod or electrode available at that outbuilding. Then a 4 wire system after the sub feed panel.

    Just like the main service disconnect for the premises.

    If I read my trivia history correctly, the 3 wire circuit for dryers, ranges, wall ovens and cooktops started during WW2 to save copper for the war effort.
    There were attempts to change this thru several code cycles but only happened about 12-15 years ago.
  • Jamie Hall
    Jamie Hall Member Posts: 23,161
    I've ordered the Littlefuse.

    The main cables are #4 copper, so that should be good. And yes, it is the older style farm wiring -- the neutral is bonded at the outbuilding sub panel, and there are grounding rods (how good they are I haven't a clue...) from that panel.

    Thanks all!
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Solid_Fuel_ManJUGHNE
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,452
    @Jamie Hall in conduit or direct buried????
  • ChrisJ
    ChrisJ Member Posts: 15,583
    edited June 2019
    If you look at datasheets on fuses you'll find how long it takes to blow at a specific current. For example 5A will take X amount of minutes, or hours etc.

    Point being they are sized to last a very long time but can still blow eventually even if nothing is wrong.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Jamie Hall
    Jamie Hall Member Posts: 23,161

    @Jamie Hall in conduit or direct buried????

    Direct buried.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England