Temperature help with Pennant hydronic boiler

Huberg
Huberg Member Posts: 2
Having issues at my work with our Pennant hydronic boiler (Model PNCH 2000). Just started here and I was told its been an issue for a while. Apparently whatever temp you set it at, it automatically heats to 180 degrees. We've had some techs come take a look and all we've gotten so far is the control guys (it's a honeywell control) and boiler guys pointing fingers at each other. Reaching out to see if anyone has had a similar issue. Sorry for the vagueness but just learning everything over here will reach out with more info as I get it. Thanks

Comments

  • JUGHNE
    JUGHNE Member Posts: 11,042
    It seems like the controls should "in control" of the boiler.
    Boiler is just a firebox needing control.
    Huberg
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,453
    You need someone with some control knowledge and an electrical meter to track down the problem
    Huberg
  • Huberg
    Huberg Member Posts: 2
    Thanks for the help! Turned out to be a bad relay in the controls.