What was the worst looking boiler you saw that was still operating?

RayWohlfarth
RayWohlfarth Member Posts: 1,459
I thought this would be futon a Sunday morning. What was the worst boiler you ever saw that was still running? I was looking over some pics of bad boilers and came across this one. It was leaking and when I pointed this out, he said it was a continuous blowdown
Ray Wohlfarth
Boiler Lessons
Canuckerdelta T
«1

Comments

  • RayWohlfarth
    RayWohlfarth Member Posts: 1,459
    Sorry I thought this would be fun on a Sunday morning Not sure where futon came from Darn autocorrect
    Ray Wohlfarth
    Boiler Lessons
  • Mike_Sheppard
    Mike_Sheppard Member Posts: 696
    edited March 2019
    Oh man I wish I would have kept all the pictures over the years. I’ll just pick a recent one. This is from last week. The one on the right still running. Glad I wasn’t there to work on that.
    Never stop learning.
  • SlamDunk
    SlamDunk Member Posts: 1,570
    Wish I had pictures. 1968 kewanee, 200HP, no water treatment, lots of leaks, lots of make up water. Came with building my company purchased. Decommisioned 2015.
  • Mike_Sheppard
    Mike_Sheppard Member Posts: 696
    Fixed the burner on this one last year. 109 years old.
    Never stop learning.
  • JUGHNE
    JUGHNE Member Posts: 11,042

    Not the oldest but maybe the ugliest.
    1955 Kewanee-Ross, 1 million plus BTUH.
    Coal to NG conversion in late 60's.
    Was retubed maybe once, because of dry firing.
    Still has cond pump from that install, (motor has been changed)
    Twice as big as needed today because of building improvements.
    1919 zone is one pipe CI rads, 1954 zone is 2 pipe convectors.
    Doesn't seem that old to me as I was in Kindergarten when it was installed, :)
    Still needs replacing.
    Alan (California Radiant) Forbes
  • Intplm.
    Intplm. Member Posts: 1,883
    Maybe it's time for another "UGLIEST BOILER" contest.
  • Canucker
    Canucker Member Posts: 722
    @RayWohlfarth I think I'm going to describe every leak I find as a "continuous blowdown" :p
    You can have it good, fast or cheap. Pick two
    ratioforesthillsjd
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,453
    @jughne,
    looks pretty good it will probably go another 60 years people say old stuff is ng if it was ng it would have been gone years ago. now we replace boilers that are 10-15 years old.

    @mikesheppard

    You got some good stuff their those old water heaters were the rage 30 years ago (the name escapes me and is going to bug me all night) hated those burners and water heaters. The old CI boiler is still going and I think I spotted a big Iron Fireman burner on that HRT. It's at least an AO (or PAO)-4-15 100 gph burner maybe bigger. AO was air atomizing (with compressor) PAO was pressure atomizing or they could be gas or combination
  • Jellis
    Jellis Member Posts: 228
    edited April 2019
    Not a boiler, but this is one of my favorite oldies, guy said he remembered when his father had it converted to oil when he was a kid and he would never replace it!



  • SlamDunk
    SlamDunk Member Posts: 1,570
    edited April 2019
    Oh, if we're going there...Had this one replaced in parent's house last summer. Year over year oil reduction to date: 70% . The burner was not tuned properly until last week of February. Looking for 75% reduction in oil consumption next winter!


    Jellis
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,453
    @Jellis & @SlamDunk

    I think you guys win the prize. Those furnaces are unbelievably inefficient. Stack temps run through the roof. Anyone still running one of those I feel bad for them.

    The old round coal boilers "pancake boilers" "snowman" or "robots" were bad too. But with those you can usually put in a smaller nozzle and do some baffeling and improve the efficiency somewhat.
    Jellis
  • SlamDunk
    SlamDunk Member Posts: 1,570
    I'll say they are inefficient.

    It is a nice thought to have simplicity but even nicer to get thru a winter using 625 gallons of oil as opposed to something north of 2300 gallons. My goal 500 gallons.
  • Fred
    Fred Member Posts: 8,542
    @Jellis , I've owned two or three houses with those old gravity hot air furnaces in them. I replaced them with new forced air but I have to say those old units were built to outlast any home. The cast iron bowl and cap inside was over an inch thick and each half weighed over three hundred pounds.
  • Jellis
    Jellis Member Posts: 228
    @Fred I couldn't find anything wrong with it, other than being inefficient and ugly.
  • jumper
    jumper Member Posts: 2,228
    SlamDunk said:

    Wish I had pictures. 1968 kewanee, 200HP, no water treatment, lots of leaks, lots of make up water. Came with building my company purchased. Decommisioned 2015.

    An abbatoire in the middle of nowhere. Steam scalds pigs and cleans premises. So no condensate return. Raw well water feed. Kewanee looked rusty but it raised steam twice a day five days a week.Was steel better in the olden days.

  • RayWohlfarth
    RayWohlfarth Member Posts: 1,459
    Sorry all I was called out of town and had no access. There are some scary boilers
    Ray Wohlfarth
    Boiler Lessons
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,459
    @Jellis and @SlamDunk Are those the boilers from Home Alone
    Ray Wohlfarth
    Boiler Lessons
    Intplm.Jellis
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,453
    Those old gravity hot air furnaces were good for one thing.

    Causing greenhouse gas emissions and a super high stack temperature
  • Lard
    Lard Member Posts: 115
    A currently operational gas-converted gravity furnace in a 1920’s house. It does have an old belt-drive blower that maybe gets it to 50% efficiency....
  • Fred
    Fred Member Posts: 8,542
    Lard said:

    A currently operational gas-converted gravity furnace in a 1920’s house. It does have an old belt-drive blower that maybe gets it to 50% efficiency....

    I can't imagine where they would have mounted a blower or that you'd want the dust it produces all over the house/walls???
  • Intplm.
    Intplm. Member Posts: 1,883
    @RayWohlfarth The worst boiler that was still working that I ever saw was a forty year old small, oil fired steel new yorker.

    It was installed in 1977. Was original to the house. And was in the basement laundry room (Of course). The homeowner was told by at least three different contractors to replace it.

    The combustion chamber was intact but the heat exchanger and the baffles were all deformed and in some weird looking state of destruction. The whole boiler was leaning to the left. It had stains from many different past repairs on the jacket. Almost all of the insulation on it was gone. It was awful.

    Her excuse to not change it was because, and I quote. "But it's still working."
    She was a neighbor and friend of ours. It took insistence from me and our friends to finally get her to change it just two years ago.

    Wish I could find the pictures.
  • @JUGHNE Now, THAT'S a boiler. It reminds me of a pot-bellied plumber.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,453
    @Fred
    I think that someone made "accessory blower" kits for those things. They sat on the floor net to the furnace and pushed return air into the furnace. HOLLAND furnace rings a bell
  • Fred
    Fred Member Posts: 8,542

    @Fred
    I think that someone made "accessory blower" kits for those things. They sat on the floor net to the furnace and pushed return air into the furnace. HOLLAND furnace rings a bell

    On the return side makes sense, I guess. Still seems like a dirty proposition. I can remember, as a kid, the dust/dirt those furnaces created. Every Spring my parents would buy a couple cans of what looked like play dough and we would take a baseball size hunk of it and roll it on the wall paper. It did a remarkable job of lifting the dust/dirt off of the wall paper. When we were done it looked like new. Part of the "Spring Cleaning" ritual.
    SeanBeans
  • lchmb
    lchmb Member Posts: 2,997
    had a slant fin boiler I was asked to inspect for heavy usage. Found the owner had installed it himself, never removed it from the wood pallet which had broken. The taco 555 zone valves were wired 110 to the t-stats. the smoke pipe was run up to the area of the chimney thimble, and missed by 6". The chimney itself was an outside chimney strapped back to the house (hung out about two foot at the top). The oil tank was sitting about 4' in the air on rail road ties... and when i mentioned all the issues to the owner he called me a thief and said the oil was junk, that's why he used so much..
    stlvortacSolid_Fuel_Man
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,453
    @lchmb

    LOL can't make it up. I would love to have pictures of that.

    Amazing more people are not killed by their heating equipment

    I am an electrician as well. People think if they turn the switch and the lights come on everything is ok.......not
    Solid_Fuel_Man
  • SeanBeans
    SeanBeans Member Posts: 520
    I like when people freak the hell out when you turn off the red emergency switch at the top of the stairs... NO!! That turns off the gas to the whole house!!
  • JUGHNE
    JUGHNE Member Posts: 11,042
    There were some after market kits around here that put a blower on top of the furnace. The shaft came out of the top dome and the motor and belt were exposed on the top.

    Some return air ducts were underfloor tunnels with wood box drops from the perimeter of the house.....lined with concrete or maybe dirt. Filters for dirt and dust?....the entire planet is made out of this stuff, this was so much cleaner than wood/coal stoves in the living area.
    For these the furnace set on top of the RA plenum.
    All supply ducts were on the inside central walls.
    (These make excellent large RA grills for upgrade to new FAF, no cutting in the existing house. Only add SA registers to perimeter.
    I leave the old BB RA grills under the old windows after blocking off the opening behind the grill.)

    Even after FAF became the standard it took at least 20 years for the trades to reverse the locations of RA & SA. (around here anyway). Old habits die hard.
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,459
    Wow those are some wild looking pictures Makes mine look tame. LOL I have this on a boiler with rollout and the owner said he didn't want to change it

    Ray Wohlfarth
    Boiler Lessons
    Solid_Fuel_ManSeanBeans
  • ChrisJ
    ChrisJ Member Posts: 15,588

    @Jellis & @SlamDunk

    I think you guys win the prize. Those furnaces are unbelievably inefficient. Stack temps run through the roof. Anyone still running one of those I feel bad for them.

    The old round coal boilers "pancake boilers" "snowman" or "robots" were bad too. But with those you can usually put in a smaller nozzle and do some baffeling and improve the efficiency somewhat.

    I still question which is ultimately more cost effective.

    An efficient furnace / boiler that you need to replace every 10-15 years, or one of the old "unbelievably efficient" ones that lasts 80-100 years.

    The cost of replacement isn't small.

    Anyone have some numbers handy?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Intplm.
    Intplm. Member Posts: 1,883

    Wow those are some wild looking pictures Makes mine look tame. LOL I have this on a boiler with rollout and the owner said he didn't want to change it

    @RayWohlfarth Did you ever have a customer say they didn't want to change something, like the picture above? Only to place blame with you weeks later, saying, "you should have changed it when you were here last time or this wouldn't of happened."
  • Lard
    Lard Member Posts: 115
    > @EBEBRATT-Ed said:
    > @Fred
    > I think that someone made "accessory blower" kits for those things. They sat on the floor net to the furnace and pushed return air into the furnace. HOLLAND furnace rings a bell

    It is indeed a “conversion blower” that sits on the floor in-line with the return. I believe the brand is ‘Viking’ or something along those lines. It even has filters believe it or not.
    The burner is a Gordon atmospheric that used to be millivolt with a Baso switch, but was at some point changed to a modern 24v combo valve. It is burning around 120k BTU/hr based on a quick meter clocking.

    The plan is to yank it out eventually and do a cast iron boiler/hot water system since the ductwork is rather sad (and asbestos-wrapped).
  • Leonard
    Leonard Member Posts: 903
    edited April 2019
    I'ld replace the melted controller on general principles.

    But thing is it'll likely work fine for years. Technically the PC board can structurally stand up to heat very well. Seems only the cosmetic protective plastic cover shrank and warped. Seems only issue is did cover try to pull off any components as it warped, and are 120 Volt wires now exposed. However plastic components (relays) under cover may have warped too.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,453
    @RayWohlfarth
    I am an easy guy to get along with (I think) but with customers like that they get the gas line and some cut and taped wires if they don't do the right thing

    @JUGHNE I think I saw 1 top mounted blower once.

    A lot of the 1950s small ranches built around here had supplies on the inside walls and returns on the exterior. Returns were always panned so every penny counted.

    The other thing around here in the 50s was aluminum ductwork made with long sweeps. Somebody told me they called them railroad fittings.
  • SlamDunk
    SlamDunk Member Posts: 1,570
    edited April 2019
    ChrisJ said:

    @Jellis & @SlamDunk

    I think you guys win the prize. Those furnaces are unbelievably inefficient. Stack temps run through the roof. Anyone still running one of those I feel bad for them.

    The old round coal boilers "pancake boilers" "snowman" or "robots" were bad too. But with those you can usually put in a smaller nozzle and do some baffeling and improve the efficiency somewhat.

    I still question which is ultimately more cost effective.

    An efficient furnace / boiler that you need to replace every 10-15 years, or one of the old "unbelievably efficient" ones that lasts 80-100 years.

    The cost of replacement isn't small.

    Anyone have some numbers handy?
    An efficient furnace you have to replace every 10-15 years.

    My numbers are:
    An average of 2200 gallons/yr @ $2.50/gallons=$5500/year *10yrs=$55,000 in fuel costs for the gravity furnace we just replaced.

    I was generous with the price for heating oil and didn't account for deep, long, cold winters. The ductwork is in place, I could buy several furnaces for $55,000.

    New furnace numbers:
    Looks like it will have used 700 gallons this season@ $2.50/gallon=$1750/year*10 yrs=17500.

    You have to look at the long picture.

    ChrisJSolid_Fuel_Man
  • ChrisJ
    ChrisJ Member Posts: 15,588
    SlamDunk said:

    ChrisJ said:

    @Jellis & @SlamDunk

    I think you guys win the prize. Those furnaces are unbelievably inefficient. Stack temps run through the roof. Anyone still running one of those I feel bad for them.

    The old round coal boilers "pancake boilers" "snowman" or "robots" were bad too. But with those you can usually put in a smaller nozzle and do some baffeling and improve the efficiency somewhat.

    I still question which is ultimately more cost effective.

    An efficient furnace / boiler that you need to replace every 10-15 years, or one of the old "unbelievably efficient" ones that lasts 80-100 years.

    The cost of replacement isn't small.

    Anyone have some numbers handy?
    An efficient furnace you have to replace every 10-15 years.

    My numbers are:
    An average of 2200 gallons/yr @ $2.50/gallons=$5500/year *10yrs=$55,000 in fuel costs for the gravity furnace we just replaced.

    I was generous with the price for heating oil and didn't account for deep, long, cold winters. The ductwork is in place, I could buy a couple several furnaces for $55,000.

    New furnace numbers:
    Looks like it will have used 700 gallons this season@ $2.50/gallon=$1750/year*10 yrs=17500.

    You have to look at the long picture.

    Ouch.

    Well.
    Like I said. I've been curious, never said I was right. :p
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    Solid_Fuel_Man
  • HotanCool
    HotanCool Member Posts: 55
    I've seen this large, old ,oil fired boiler, in a large 1900s apartment home. It was literally built into the brick wall! 3.50 or 5.50 gallon nozzle I think. Maybe even a dual nozzle setup. Can't remember exactly,but the cleaning access doors weighed more than Volkswagen. A little scary!
  • RayWohlfarth
    RayWohlfarth Member Posts: 1,459
    @Intplm. @Leonard We were giving them a price on a replacement boiler. I made sure I sent an email to the boss and let him know. I didn't get the project