Type of water to use

Options
RWALD
RWALD Member Posts: 21
I run triangle tube boilers is it ok to use RO water in the system? I have floor heat and fin pipe.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,284
    Options
    Yes -- but you will want some sort of corrosion inhibitor and pH buffer in the system. RO is pretty "hungry" (but not as aggressive as DI)
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • RWALD
    RWALD Member Posts: 21
    Options
    Ive had multiple heat exchangers start leaking in the units. They are 399 btu Natural gas units. I run fernox in the system. System's been goin on 3 years now
  • nicholas bonham-carter
    Options
    Does the floor tubing have an Oxygen barrier?—NBC
  • RWALD
    RWALD Member Posts: 21
    Options
    Yes it is Oxygen Barrier pex a
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    Options
    May be time to send a water sample to a lab and see what is the best direction to go as far as treatment/adding chemicals.
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • hot_rod
    hot_rod Member Posts: 22,139
    Options
    RWALD said:

    Ive had multiple heat exchangers start leaking in the units. They are 399 btu Natural gas units. I run fernox in the system. System's been goin on 3 years now

    There was a batch of short life heat exchangers on the market a few years back, weld issues. Contact the rep to see if yours are in the date code range.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream