Can't get Auto mode to work for Air Handler Blower

Roobul
Roobul Member Posts: 39
edited November 2018 in THE MAIN WALL
I have a Unico air handler with a hydronic heating coil, 24V control circuit with Therm-O-Disc time-delay relay. When the thermostat Fan switch is turned from Auto to On, I see 24 volts move from the blue to the green terminal and the blower relay is activated - fan comes on, no problem. In order to use Auto mode, I strapped a JC/Penn Aquastat A19DAC-1 to the supply pipe, and connected its Red (common) and Yellow (close at temp) to the same bus bar terminals as the thermostat's Blue (load) and Green (fan) -- in parallel with the thermostat's "Fan On" circuit -- and the transformer's primary coil blew. Same result on both air handlers, so it's not a matter of one faulty component or wire. There is no continuity between the Aquastat's terminals and ground, when cold or hot; no indication of a short anywhere. If I put a jumper across the same (blue and green) terminals of the bus bar, the blower comes on. Why would the Aquastat cause this problem when it's in parallel with the thermostat or a jumper? Any ideas would be greatly appreciated.

Wiring Diagram attached:

Comments

  • HVACNUT
    HVACNUT Member Posts: 5,804
    Because its back feeding through the fan relay.
    What was the disc aquastat wired to?
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,455
    Looks like it should work but you may have other items not shown which could be causing the problem. I suspect all is not shown

    You could wire the aquastat to terminals #1 &#2 on the fan relay. This is 120 volt wiring not 24v. also make sure the aquastat will handle the motor amperage if you go this route
  • unclejohn
    unclejohn Member Posts: 1,833
    Can you set up your thermostat for electric heat?