Low Water in Boiler - Wet Steam Likely
I have noticed water slow to return to boiler. Most times, boiler shuts off after 15-20 minutes because LWCO trips. Last year I had our friend Ryan at New England SteamWorks out for maintenance and he disassembled the wet return (which is all above ground by the way) and found some sludge. He added spigots at each 90 for flushing. Didn't really have too many LWCO occurrences. I did however notice water level surging so I skimmed 4-5 times. Still notice a lot of water "spilling" into the sight glass so I installed a ball valve on the lower portion of my sight glass to check for wet steam. 9/10 times when its steaming and I close lower sight glass valve and open ball valve, I get a slow trickle of water. Never added any additives to boiler water. Always flush with utility pump once a year in fall. Just flushed now and wet returns are clean, no blockage.
I'm thinking wet steam is the culprit. Water level generally is pretty stable when its steaming, bounces the normal +/- 1/2". As you can see in pictures, I don't have it over filled, its right in middle of sight glass. Boiler won't run more than 20 minutes without LWCO now. Soon as it trips, water returns back to normal level within 5/10 minutes.
I know that this boiler with the side tappings are nobodies best friend, especially steam's. Anyone got any ideas?
She just fired up and soon as steam is produced, water level surges a good 1" in sight glass. This time, no LWCO, stat turned it off. As soon as boiler shuts down, water level drops more.
Can you get Ryan back? You should get him back to clean and adjust the boiler and burner anyway, if you haven't...Br. Jamie, osb
Here are the main vents. I only have one main. Only had the VentRite No. 35 on there for the longest time until I got smart and added more.
How long is your main, plus dry return?
Do you ever see the gauge needle moving below positive pressure, at the end of the burn?--NBC0 -
I agree with @Nicholas Bonham-Carter that it could be vacuum in the system hanging up the condensate. Maybe at the end of the dry return install a good quality Y pattern check valve on a tee near your air vents. Check valve must be level 1/2" ips is ok. Or you can buy a steam vacuum breaker. This will let air in if you system goes into a vacuum-1
NBC/Fred, believe you guys might have helped me here. I added a support on the return line which looked like it needed pitch, and last two burns have been turned off by tstat. I am still noticing the water level dropping more after boiler shuts off. This trips the LWCO. I’ll try to get on Ryan’s long list of low priority jobs and see when he can come consult.
I can hear the main vents hiss considerably as soon as boiler turns off.-1 -
One other thing I'm noticing. That Hartford Loop looks to be well above the boiler water line. If so, that may be letting pressure push water away from returning to the boiler. When was the last time the pigtail that the Pressuretrol is mounted on, was cleaned out? If it is clogged, the boiler pressure may be higher than you think, adding to the problem and maybe why the main vents are noisy at the end of the heating cycle, sucking air back in.1
I replaced the pigtail last year which was in fact completely clogged. Haven’t taken it out this year yet but will check soon.0
What about that Hartford loop? Is it above the boiler water line?0
Just measured and It’s 2” below the waterline which is in the center of the sight glass.0
@joshpjost,
Let me have your ear for a moment. You have a few decent clues the way I am looking at it.
1. slow condensate return...could be a vacuum issue
2. Noticeable hissing steam vents on shut down... air trying to get in to break the vacuum
3. Water level drop and trips LWCO on shut down.....When the burner shuts down the steam in the boiler and piping condenses and pulls the system into a vacuum. The reduction in volume of changing steam to water is a reduction in volume of 1700. The rapid drop in pressure from a positive steam pressure to a vacuum causes some of the water in the boiler to instantly change to steam as the pressure drops and this steam quickly causes water in the boiler to evaporate lowering the water level.
Could it be another problem? Yes But to me it points to vacuum
Makes sense to me. Barnes & Jones vacuum breaker right next to the main vents?0
I put a ball valve at the end of the main vent antler and opened it right as the tstat shut her down. No change to water in sight glass, still dropped after shutdown and triggered the LWCO, not that it matters. I still plan to put a check valve there on the antler just in case there is a vacuum condition.EBEBRATT-Ed said:@joshpjost,
Could the surging I notice once it starts steaming be the rise in water level with the nucleation of water vapor bubbles? This would also explain the water level decrease when the boiler shuts off. I've skimmed twice already this year just to confirm no oil in the water.
How did you skim and for how long? The skim has to be very, very slow and can take several hours. Surging, low water, water droplets on the top portion of the sight glass are all indications that a skim is needed. Did you skim after the antler or any other piping work was done? Even the little new piping for that antler will put oils back into the water.0
You could try the vacuum breaker or equal measures at the boiler itself. See if that does anything different. I tried a vac bkr at the boiler but it takes a high level of vac to pull it open.
It is a long ways from the air vents back to the boiler gauge.0
- 85.2K THE MAIN WALL
- 55 Biomass
- 73 Chimneys & Flues
- 130 Geothermal
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 884 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 59 Water Quality
- 49 Industry Classes
- 89 Job Opportunities