New Vaporstat installed system pressure question
borner
Member Posts: 19
Hello!
I was waiting for the warm-ish weather so I didn't freeze if I messed up, so today I installed my new vaporstat and 16oz gauge.
The pressure builds up to 10-12 oz while venting the main (1 gorton #1).
After the main closes, pressure holds steady at 8-9oz while the radiators warm up. (its about 63F out / in side.. but wanted to test) All rads have new Hoffman 1A's.
That sounds high after reading everyone else's experiences.
Seems like I need more main venting, maybe another #1 (or more). Does that seem correct?
Also all my Hoffmans are set around "1" - "2" and radiators heat up pretty evenly. Can I just adjust them all up evenly, shift to "3" - "4" to keep the pressure lower?
Thanks for all your help, you guys are amazing. Also included a picture of the new set up, because I'm a little excited about it
Bret
Bret
How long are the mains and what diameter pipe? A Gorton #1 is very little venting unless your mains are no more than about 10 ft of 2" pipe. That's about what a Gorton #1 can effectively vent.You always want to vent the mains fast. You really can't over vent them but you reach a point of no return on your investment.
As far as the Hoffman 1A's. A setting of #3 is about the same as a Hoffman #41 which is a slow vent. I would set most of your radiators at #3 and those that are larger rads or further away from the boiler at #4 or maybe even #5.0 -
Ok, that makes sense. The main is about ~23-25' of 2"
Sounds like I need a 3-point (if you will) antler of Gorton #1s
Thanks for your insight!0 -
One Gorton #2 or a Big Mouth would do, too.borner said:Ok, that makes sense. The main is about ~23-25' of 2"
Thanks for your insight!Br. Jamie, osb
Big mouth, I like the sound of that. I can't seem to find them at Supply House... Is that the actual name of the vent?0
The Barnes and Jones Big Mouth is a far better vent that the Gorton #2, In my opinion. It is all Brass construction, vents at double the capacity of the Gorton #2 and costs a little less. Here is the link:
https://www.amazon.com/s/ref=nb_sb_noss/147-3054328-0942228?url=search-alias=aps&field-keywords=Barnes+and+Jones+Big+mouth+vent0 -
Only problem with the Big Mouth is it doesn't close against rising water, so if something goes wrong you'll have a major leak. If your "A" dimension (height of the lowest steam-carrying pipe above the boiler's waterline) is marginal (less than 28 inches) I'd stay with the Gorton.
And the Gorton is all-brass too.All Steamed Up, Inc.
Consulting0 -
The Gorton #2 is all brass?Steamhead said:Only problem with the Big Mouth is it doesn't close against rising water, so if something goes wrong you'll have a major leak. If your "A" dimension (height of the lowest steam-carrying pipe above the boiler's waterline) is marginal (less than 28 inches) I'd stay with the Gorton.
The #1s I have feel and sound like painted steel?
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Try a magnet. The G-2 I just checked is not steel. Could only feel some steel thru the case around the top.
I would call it brass with some steel parts inside. Could be some type of stainless steel inside that can be magnetized.0 -
Might be the seat. Some trap manufacturers did this too, since that's where most of the wear occurs.All Steamed Up, Inc.