hw boiler code PA
HEATON
Member Posts: 118
Does anyone know if the code, (L&I boiler division), requires a secondary limit control on residential boilers? PA installation. Thanx JH
Would the operating control count as one and the high limit count as the secondary limit??
I know NE is a long way fm PA, but this state boiler inspector is requiring a secondary manual reset limit for commercial boiler that I hope to fire up next week. It will have outdoor reset control and operating control....both original. A man reset with insertion probe into the water, not strap on, has to be added.
Also man reset LWCO.
Again commercial and from a state that probably requires less safety controls than yours. FWIW0 -
Residential...nope, according to NFPA. Just a limit control and a low water cut-off, properly installed. But it also depends on the AHJ. If they want one, you're probably going to have to put one on.steve0
and a back flow preventer0
In my case the local water supplier wants a testable BFP.
It had none at all other than the pressure reducing valve since 1963 and is in a nursing home.0
- 85.2K THE MAIN WALL
- 55 Biomass
- 73 Chimneys & Flues
- 130 Geothermal
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 885 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 59 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements
