Height of pressuretrol
Stangob
Member Posts: 26
Hello all just looking for verification that my pressuretrol is ok. I installed a pressure gauge as recommended and used a 3 inch nipple off of the pigtail. Just wondering if I should change it to a close nippe or is it fine as is. Thanks in advance for the advice.
It's fine. Height of the pressuretrol -- so long as it is above the water line -- doesn't make any difference.Br. Jamie, osb
Thank you Jamie. It puts my mind at ease. Now I can finalize install without wondering.0
Is that installed on a skim tapping?
I would've used a tee instead of an elbow if that's the case.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
No the skim port is on the other side of the boiler. This is a Burnham IN50
That looks good but I would have put that 0 - 30 PSI Gauge on a Tee and added a 0 - 3 PSI gauge next to it. The 0-30 is required by code but really doesn't allow you to see what the boiler is doing on a normal heat cycle. A 0-3 PSI gauge is sensitive enough to allow you to make sure your Pressuretrol is functioning like it should.0
Hi Fred. I have a 0-30psi gauge installed as well but elected not to try and unscrew it. Also I was thinking let the gauge see what the pressuretrol is seeing. I was thinking along the lines of what if the 0-30psi pigtail gets gunked up it would be on a different pigtail than the pressuretrol0
Sorry! My old eyes aren't what they use to be. Upon closer look, I see that is a 0 - 3 PSI gauge you mounted on the pigtail with your Pressuretrol. That is the right way to do it (I was thinking that was your 0 - 30 PSI Gauge)Stangob said:Hi Fred. I have a 0-30psi gauge installed as well but elected not to try and unscrew it. Also I was thinking let the gauge see what the pressuretrol is seeing. I was thinking along the lines of what if the 0-30psi pigtail gets gunked up it would be on a different pigtail than the pressuretrol
It's ok Fred. The fact that you wanted to make sure everything is ok is why I keep coming back to this site for trusted advice. Thank you0
- 85.2K THE MAIN WALL
- 55 Biomass
- 73 Chimneys & Flues
- 129 Geothermal
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 884 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 59 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements
