closing off steam radiators not in use
Hello all my question is this.
I purchased a home with an old boiler steam heat and radiators that are cast iron I think..
my problem is that downstairs the radiators get nice and hot but upstairs they stay cold except for the one in the upstairsbathroomit gets hot... I was thinking if I closed all except the one upstairs in bedroom and the one in living room that it would allow those 2 to get hot... all the vents are new btw
«1
  • KC_Jones
    KC_Jones Member Posts: 5,739
    You have an imbalance/venting issue. Closing off radiators will only make your boiler act oversized and not necessarily do anything for the balance issue. The vents being new doesn't really have anything to do with it, they need to be the right SIZE vents. New old doesn't really matter for balance. And another question how do you propose to heat the house with only those 2 radiators turned on? What size main vents do you have? What type and size of vents do you have on the radiators?
    2014 Weil Mclain EG-40
  • richrego
    richrego Member Posts: 22
    I thought by closing off everything but the living room and bedroom I got get heat to those 2
    I do not know what size main vent I have and I believe the vents on the radiatorsare vent rite number 1 or 11 something like that
  • richrego
    also wondering if closing other radiatorswill create a problem like pipe bursting or something
  • KC_Jones
    You will get heat to those 2 if you do that, but you won't get any heat to anywhere else. The main problem here is a balance issue. You need good main venting to get all the air out of the mains as fast as you can. After that you need to balance the radiator venting. Since you have the ventrite vents you can adjust those. In general you want to vent faster on bigger rads that are further from the boiler and closer smaller rads you vent slower. You could start by turning the vent up on ALL the second floor rads and turning down all the ones on the first floor, BUT you must make sure your main venting is in order first. Closing a rad won't create a pressure problem per se other than making the boiler short cycle on pressure. Also since most radiator valves are old and don't work so well what generally will happen is the rad will slowly fill with water. The steam can usually still seep in, but the water won't easily flow out. The only PROPER way to address your problem is sorting out the venting.
  • richrego
    OK so do u think my main vent is bad. also I have a one pipe system should I only have 1 main vent
  • KC_Jones
    You need to post details of your system, every system is different. Pictures would help. Post some pictures of the boiler and piping and the main vents in the basement. The length and size of the main pipes determines the size and quantity of vents that you need. So you would need to measure the length of the mains and what size they are and we could probably advise how to proceed. Do you have any other issues with the system? Is it quiet? Do any vents spit water?
  • richrego
    how would I know which are the main pipes
  • KC_Jones
    Take some pictures of the boiler and the piping and we can point you in the right direction.
  • richrego
    here are some pic tried to read the main vent looks like it Donley or dole that's it
  • BobC
    BobC Member Posts: 5,478
    There are problems with the way that boiler is piped, it does not have a header but will probably work because it's old and has a large steam chest. When that boiler is replaced it will need a proper header because new boilers have much smaller syeam chests. It looks like the boiler is connected with a bullhead T into the steam mains it's important those mains are sloped right so water can find it's way back to the boiler.
    The large pipes covered with insulation are the steam mains. the smaller pipes that run along them are the returns while the pipes that come off the mains at a 45 degree angle are the radiator runoffs.
    What make and model are those main vents and how long is each steam main? The vents are new but they may be too small to get the air out quickly. You want to get the air out of those mains as fast as possible. Get the mains venting fixed before adjusting the radiator venting.
    Bob
    3PSI gauge
  • richrego
    how would I go about measuring each? STEAM MAIN . I WAS TOLD WHEN THEy REMOVED THEy ASBESTOS IN THEBASEMENT THEySAID IT WAS ABOUT 120 LINEAR FEET
  • KC_Jones
    You measure from where the boiler connects to the system (see picture). You measure from each side of that tee and measure all the pipe until you get to the last radiator connection, then measure the other side of the tee until you get to the last radiator connection. You will have 2 measurements and those are the lengths of your mains, then you need to know the pipe diameter of those mains and the venting can then be sized accordingly. I would recommend you educate yourself on your system. Does that boiler have a float type low water cut off? If so that needs blown down regularly, do you know about that? You also have a VXT auto feeder that can track water usage which is important as excess water usage rots out a boiler. If you don't understand your system very well it might be a good idea to purchase the books on this site and learn about it. We Got Steam Heat and The Lost Art of Steam Heating are 2 good ones. A boiler needs care and attention.
  • richrego
    Kc.
    OK blow down I have never done it we just purchased home in March and from service records I have from past owner only thing done was routine cleaning of soot and ash and nozzle and filter changes. I don't know anything but the vxt box except that the digital numbers never change always at 88.. the side sight glass is clean and at the fill mark
  • richrego
    We are looking into changing boiler because of age and the inspector recommended said it would fail soon
  • richrego
    The tech that came out and gave me a price for the boiler gave me 2 options either just do the boiler and keep steam and radiators for 4500 or 6000 for new boiler and remove all the radiators and make it a forced hot water system with baseboards which would be best in your opinions
    j a_2
  • KC_Jones
    If they are suggesting removing the steam I would probably find a new contractor. They are suggesting that most likely because they don't know steam and have. Where are you located we may know a good steam man in your area to recommend to come out and give you an evaluation. I am not saying it isn't going to fail, but just because the boiler is old does not mean it's going to die soon. Some of those old boiler are built like tanks and last for a LONG time. Also we do not discuss pricing on this site.
  • Fred
    Fred Member Posts: 8,542
    Keep the steam and make sure whoever installs it does so by the Book (the installation and owners manual that comes with the boiler). The way this boiler is currently piped, you are going to have a difficult time trying to balance the system and get steam to every radiator in a reasonable amount of time. Most likely the largest/nearest radiators will heat first and by the time those are filled with steam, the thermostat is satisfied and the boiler shuts down before the other radiators can get hot. I'm betting the radiator in the room that has the thermostat is one that gets hot, right?
  • richrego
    Oh ok sorry about the pricing thing... I am in Rhode Island I used the find a contractor but came up with Nutting
  • richrego
    He suggested I could either keep the steam or convert it to forced hot water
  • richrego
    Fred ur right
  • Fred
    richrego said:
    Fred ur right
    If your new radiator vents are adjustable, set it at the slowest setting for the radiator in the room with the thermostat. That will slow the amount of heating in that room, maybe enough for some of the other radiators, that are cold, to start to heat up. This may be an interim solution until you can get the Near boiler piping corrected and get enough main venting on the mains. Obviously the best fix is 1) get the near boiler piping installed with a proper header and two risers out of the boiler, 2) seperate the mains that go in two different directions and carry each of those down to the new header, 3) put enough Main venting on each of those two mains to get the air out of them as quickly as possible (a rule of thumb is the equalivent of one Gorton #2 vent for every 20 feet of 2" Main. Each main is vented seperately), and 4) then balance the venting on each radiator so that steam gets to each of them at about the same time (or close enough that you are satisfied with the output in each room).
    You really don't want to close any of the radiators off completely (at least not more than maybe one radiator) because that will cause you boiler to be over-sized (it probably already is so you will only compound that problem) and cause it to short cycle. With the piping the way it is right now, that will just add to your problems.
  • richrego
    What is short cycling
    I have 8 radiators I closed all but 4
  • BobC
    Short cycling occurs when the boiler shuts off on pressure before the thermostat is satisfied. A little short cycling is ok, but if it's excessive it's a problem.
    It can be caused by a boiler that is to big for the radiation attached to it or by main vents that are too small for the job.
    By closing off half the radiators you have forced the boiler to short cycle.
    Bob
    3PSI gauge
  • richrego
    Ok so now I don't know what to do I don't need heat in the 4 radiators I shut off not using those rooms
    But I do need heat in the living room with the thermostat and the bedroom upstairs
    And 2 bathrooms
  • BobC
    You should get new main vents installed first, the ones you have are much too small. Then I would try putting Very small vents on the radiators you don't want to heat up fully, you may end up putting TRV's on those and setting them for lower temps.
    Then you will have to balance the rest of the system by playing with the vents on the remaining radiators, what kind of vents do you have now? If they are adjustable you can try starting low and increas the vent rates on the rads that seem slow to heat.
    Bob
    3PSI gauge
  • vaporvac
    vaporvac Member Posts: 1,520
    edited October 2015
    Perhaps a pic of a typical rad would help. Also with one pipe, turn the vent upside-down as opposed to off. You need to fix the main venting in the basement first, however as hort-cycling wastes a lot of fuel and can stop rads from getting heat.
    Btw, a blow-down is something YOU as a homeowner need to do regularly, not something the yearly maintenance co. does. It would never show up on any paperwork as it's assumed it's being maintained. This is to clean gunk out of the LWCO so it shuts down the boiler in case of a LW situation so it doesn't boil dry. It's a safety issue. Are you saying you've never done this?
  • richrego
    I have not and I am sure the past homeowners did not either not sure though. This thing is a rusty thing so open
  • richrego
    I will take a picture of the radiator in the living room with the thermostat
  • richrego
    here is the pic of the living room radiator vaporvac
  • ChicagoCooperator
    ChicagoCooperator Member Posts: 355
    vaporvac said:
    Also with one pipe, turn the valve upside-down as opposed to off.
    The vent, not the valve (in case that wasn't obvious).
  • vr608
    vr608 Member Posts: 144
    Here's a question; I'm guessing by turning the vent upside down the boiler "sees" the same load? I thought steam was denser than air? Or is the load simply based on pressure?
    Peerless 63-03, 118,000 BTU (308 sqft), single-pipe steam system connected to 286 EDR of radiation, 30ft of baseboard and indirect DHW
    3PSI gauge
  • vaporvac
    Yes that's what I meant to type. I really need to edit.
    Jamie Hall Member Posts: 23,324
    The density of steam -- and air -- depends on the temperature. Actually, dry steam is less dense. However it doesn't really matter. By turning the vent upside down -- which keeps it from venting -- the boiler will see a smaller load, as the radiator(s) with those vents won't be able to vent the air, and hence won't be able to accept much steam.
    Keep your pressure low!!! The cutout device on the boiler should turn it off when and if the pressure reaches 1.5 psi, no more than that.
  • richrego
    Ok the vent is the silver thing on the right that looks like a ullet right... by turning them upside down won't water piss out of it
  • vr608
    From what I understand, since it won't vent when mounted upside down, in theory no water should be released.
    3PSI gauge
  • vr608
    Jamie, so what is the difference between closing the shutoff valve and mounting the vent upside down (operational state of the shutoff valve aside)?
    3PSI gauge
  • Abracadabra
    Abracadabra Member Posts: 1,948
    If your shutoff doesn't completely close against steam, it may trap condensate in the radiator causing some hammering. Also, the radiator will heat if the shutoff leaks. Vent upside prevents air from leaving the radiator and therefore prevents steam from entering.
  • vr608
    edited October 2015
    I guess my question is, assuming you had a brand new shutoff valve, is there a difference between closing the valve and mounting the vent upside down from the perspective of the boiler?
    3PSI gauge
    No. But this assumes that the brand new shutoff valve closes steam tight, and stays that way, every time. One can buy valves which do that. One can also buy, for a lot less money, valves which don't...