I am installing two Utica SSC Boilers, has anyone had any experience common venting high efficiency boilers? Has anyone had any problems with the special check valves for this purpose? Utica tells me that I can do this.
Thanks, Bob Gagnon
To learn more about this professional, click here to visit their ad in Find A Contractor.

Comments

  • kcopp
    kcopp Member Posts: 4,432
    Options
    I did not think that common venting was allowed w/ CAT IV(4)appliances.
    If it was it would sure help me in a few applications.
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,541
    Options
    http://www.ecrinternational.com/secure/upload/document/3873.pdf
    Page 30 explains common venting requirements
    To learn more about this professional, click here to visit their ad in Find A Contractor.
    jonny88
  • todd_ecr
    todd_ecr Member Posts: 92
    Options
    Bob, you can common vent the SSC boiler. The venting must be done entirely in polypropylene. You may use PVC for the intake. An important consideration is the amount of room you have available above the boiler as the check valve can use up to 2 feet of that space vertically.

    I've attached the check valve kit instructions. You will need 1 check valve kit for each boiler. Also, if you intend on cascading these boilers together, don't forget the System sensor kit.
  • Henry
    Henry Member Posts: 998
    Options
    In Canada, the new B149.1-15 will allow common venting but needs to meet clause 8.10.6
  • Henry
    Henry Member Posts: 998
    Options
    Here is the 2015 info