Do I need this F&T?

Timco
Timco Member Posts: 3,040
We are re-piping this from the vert section to the boiler, about 20' away. If I fix the pitch, do I need the drip / trap?
Just a guy running some pipes.

Comments

  • Steamhead
    Steamhead Member Posts: 16,796
    Maybe.

    What happens on the other side of that brick wall? Does the pipe pitch down from outside as it enters the building?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Timco
    Timco Member Posts: 3,040
    It pitches back towards the boiler and we can repipe to make sure it has pitch all the way back.
    Just a guy running some pipes.