Vision Pro 8000 thermostat
Options
Silvion
Member Posts: 26
I have a vision pro 8000 for steam heat. I have it set to 1 cph per hour cycle. However went it calls for heat when there is a 2 or 3 degree setback it keeps running and short cycling until the temp is met. Is there any other setting I need to adjust. System type I set to 3 Heat only. Its a oil steam furnace. I just want it to run once for the hour fill radiators with heat then shut off.
Thanks
sil
Thanks
sil
0
Comments
-
Any thermostat setting is just a pre-programmed "guess". It's not an accurate setting. Short cycling is typically caused by an oversized boiler, undersized venting, or improper piping.0
-
or, sometimes, improper pressure settings. Though less often than a somewhat oversized boiler or undersized venting, which are the two most common culprits.JStar said:Any thermostat setting is just a pre-programmed "guess". It's not an accurate setting. Short cycling is typically caused by an oversized boiler, undersized venting, or improper piping.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 423 Carbon Monoxide Awareness
- 71 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 60 Pipe Deterioration
- 850 Plumbing
- 5.8K Radiant Heating
- 375 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 55 Job Opportunities
- 18 Recall Announcements