Table for calculating volume of air per linear foot in various pipe sizes
Anyone have a chart showing the amount of cubic feet of air per linear foot of pipe for various pipe sizes? I'm specifically looking for 1-1/4" and 1" IPS, but would love a chart for other sizes as well. Sizing my radiator vents using the master venting principles outlined in Gerry Gill's and Steve Pajek's article. Thanks.
  • SteamworkS
    SteamworkS Member Posts: 14
    Sorry, I didn't look at the last page on Gerry and Steve's article. So I have all the values EXCEPT the amount of air per linear foot in a 1" pipe. Thanks
  • KC_Jones
    KC_Jones Member Posts: 5,885
    1 1/4" and larger is already in Gerry and Steve's balancing steam (pg 14) which it sounds like you already have. For 1" pipe it would be .006 cu/ft per linear foot of pipe.
    2014 Weil Mclain EG-40
  • SteamworkS
    Thanks KC.
  • JStar
    JStar Member Posts: 2,752
    edited September 2014
    If you don't have the charts handy, I've found a reliable rule-of-thumb to be 0.1 ft3 of air for every 10 feet of 1" or 1-1/4" radiator run-out. I usually remember it as 0.1 per floor.