tenant heat metering

rjncontrjncont Member Posts: 1
what is an accurate means to meter tenant heating from a central heat source (oil boiler)? all units are zoned individually 

Comments

  • RichRich Member Posts: 2,220
    edited March 2014
    Taco

    Iworx system can be part of the system also because nobody will just take your math at face value .  You will also require a KNOWN Delta T . There are a few choices of circulator that will closely control Delta T . Taco VDT and Bumble Bee , also Wilo Stratos with IR option .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC 732-751-1560
    Serving most of New Jersey , Eastern Pa .
    Consultation , Design & Installation
    Rich McGrath 732-581-3833
  • Big EdBig Ed Member Posts: 863
    Tenants

    We all know the best option is a separate boiler and oil tank
    I have enough experience to know , that I dont know it all
  • maine rickmaine rick Member Posts: 107
    control

    we use Honeywell AQ control with communicating thermostats. you can set the max temp and check the amount of hours each zone runs. also is outdoor reset ready.