New Furnace Setup - What do you think?

Hello HeatingHelp!

Your advice on venting has been impeccable this far.  Can you please take a look at my current steam furnace setup?  I recently converted from Oil to Gas and wanted to know your thoughts on my current setup.

Thanks!
«1

Comments

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,576
    New gas boiler

    Was the new boiler properly sized from the EDR of the radiators?

    Does the supply piping conform to the manufacturers requirements, in regard to layout, and pipe diameters (the riser, and header look small)?

    The tee on the main should probably be eliminated, and each branch separately connected to a separate takeoff from the header.

    How is the state of your main vents? When you are satisfied with the piping, then you can insulate the pipes. Have you run it yet?--NBC
  • Re: New gas boiler

    Please note: I didn't install the boiler myself.  The oil to gas conversion company installed it.  I firmly believe that they sized up the boiler from the EDR of the radiators. 

    I do not know if the supply piping conforms to the manufacturer's requirements.  I can only assume.  The boiler is:  BRYANT  BS2 (BS2AAN000187ABAA)

    I can suggest to the installer to eliminate the tee.

    I don't think I have any main vents.  I found, what I believe to be 1 vent at the other side of the basement (hidden behind a drywall, of course).  It is the only vent in the basement.  It looks like it sits on top of the wet or dry return.  I would like to add some main vents, but will seek a Steam Expert soon to do that.

    I did replace all my radiators vents with VentRite Adjustable #1s and balanced my heat pretty good.
  • Steamhead
    Steamhead Member Posts: 16,796
    That's actually a Dunkirk

    with Bryant's name on it.



    These boilers are extremely sensitive to improper piping. From what I've seen so far, the piping looks too small. At least they didn't use copper on the steam piping.



    Can you post some side-view pics of the boiler, so we can see what happens when the piping leaves the boiler?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Re: Dunkirk

    Hopefully, these pics will help you!  
    Kahooli
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,576
    Photo gallery

    Can you take a picture of the riser pipe as it exits the boiler, to make sure the pipe is the full diameter of the cabinet cutout?

    Measuring the circumference of the pipes (risers and horizontal header) would be even better, as we can convert those measurements into diameters.--NBC
  • Steamhead
    Steamhead Member Posts: 16,796
    edited October 2013
    Too small

    in the third pic you can see there is a bushing behind the steam outlet elbow. They dropped it from 2-1/2" to 2". FAIL.



    I tried to attach a PDF of the piping diagram, but it didn't work.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Rod
    Rod Posts: 2,067
    Dunkirk Piping Diagram

    I think this may be the piping diagram that Steamhead is referring to.

    I've also attached table which will help you determine the pipe sizes. Measure the circumference of the pipe and consult the table for the pipe size.

    - Rod
  • Re:Too small

    Oh my!  These are serious allegations!  This boiler was just put in!  If you are correct in saying that a bushing was placed to reduce the piping from  2-1/2" to 2" then I am going to have a helluva time trying to tell my installer that his job was done incorrectly.

    What are the implications if the piping was reduced?  More energy wasted?  Less heat?

    Do you roughly know the cost of re-plumbing everything?  Is that even possible?

    Thanks for all your help and insight.  I really appreciate it, but getting quite concerned now about my new system and the upcoming winter.
  • FAIL

    When you say:

    'there is a bushing behind the steam outlet elbow. They dropped it from 2-1/2" to 2". FAIL.'



    How much of a FAIL are we talking about here?  Should I have the whole thing re-piped?  Please advise.



    Thanks!
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,576
    Installation FAIL

    The installer should follow the boiler installation manual in regard to pipe sizes, and layout. Don't listen to any nonsense about "I've been putting in these here boilers for 20 years, and I know---etc"

    You will have wet steam, and an unsteady waterline if the pipes are too small.

    It needs to be re-piped, and since we don't talk pricing here, we can't say how much it will cost, but surely an honest installer will make things right?--NBC
  • FAIL

    I'm not sure how I am going to convince my installer to change his piping?!?! He is going to think I am nuts! An amateur on heatinghelp.com is going to ask him why he placed bushings to lower the pipe size from 2 1/2" to 2"?



    This is going to be some hoot! I think I should hire a steam pro to call this dude!



    :-(
  • JStar
    JStar Member Posts: 2,752
    Steam

    Show him the manual. The boiler needs to be installed like the manual in order to qualify for warranty claims. This is no light matter. He has to fix it.
  • SWEI
    SWEI Member Posts: 7,356
    Simple question

    Was this boiler installed in accordance with the manufacturer's minimum requirements?
  • Rod
    Rod Posts: 2,067
    BS2 I&O Manual

    Hi- You didn't mention whether you had an installation manual for your new boiler. As the Bryant website doesn't have I&O manuals available, I've attached one for the BS2 below.

       If you look at the piping diagram on page 8, it gives the pipe size requirements.  You best approach would probably be that as the owner, you have the right to expect that the boiler will be piped according to the instructions in the manufacturer's installation manual and that since the piping is smaller what the manufacturer recommends, it needs to be corrected.

    Keep in mind that the manufacturer's recommendations are usually minimums rather than optimums.

    Good Luck!

    - Rod
  • JStar
    JStar Member Posts: 2,752
    edited October 2013
    Piping

    Here's the same boiler (different name) that we recently repiped.



    2-1/2" boiler risers. 3" header.
  • Pipe Size Question...

    Ok...ok...after let's take a 2nd look at this pic...

    now, please bear with me...I don't know anything about measuring pipes...but the circumfrance of the outside pipe on what I believe to the riser pipe measures:

    8 inches

    The riser pipe itself looks like it measures 2 1/2 " going across...I had my wife eyeball it with my tape measure and she confirmed what I thought as well...

    in my amateur opinion...it looks like the riser pipes (the ones coming out of the boiler at the top) measure at 2 1/2 inches...

    so...my installer may have done the job right after all? 

    I did notice the pipe at the bottom...near the Hartford loop...come out of the boiler are about 1 1/2 inches or 5 1/2 inches around the pipe...

    But I am assuming the concern at the moment is whether the riser is 2" or 2 1/2"

    please take a look at this closer photo...it shows the sign behind it that says:

    Attention: Be sure to plug unused 2 1/2" supply and return connections before filling boiler.  Plugs are furnished.

    Please let me know what you think before I make a fool out of myself with the installer!

    Thanks again steaming experts!
  • kevin_58
    kevin_58 Member Posts: 61
    pipe size

    If it says to plug unused 2 1/2 steam tapping then it is 2 in because you can clearly see they used a bushing at tapping.
  • Steamhead
    Steamhead Member Posts: 16,796
    Pipe sizes

    are expressed as inside diameter, rather than outside diameter. On this type of pipe the walls are 1/8" thick, so the outside diameter would be 2-1/4".



    It's 2" pipe, should be 2-1/2" inside diameter. FAIL.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,576
    What size pipes ??

    The measured size of the pipe is the internal diameter, so if you measure the outside diameter, it will not be correct.

    It looks as though the tapping in the block of the boiler is 2.5 in, and therefore, any sort of bushing will have reduced the diameter of the risers.

    Measure the outside diameter, and let us know what that is and we will tell you what the effective (internal diameter) is. It's quite likely that the installer has used the less expensive smaller pipe on your boiler, and with the results of that being bad, you may want to get this corrected by the installer before the winter sets in and he gets busy.--NBC
  • Rod
    Rod Posts: 2,067
    Measuring Pipe

    Hi- Take a look at the Pipe Chart I attached to previous answer above titled “Dunkirk Piping Diagram”.

      As you will see in the above chart:

     2 inch  pipe has a circumference of 7.461 inches.

    2½ inch  pipe has a circumference of  9.032 inches.

    These measurements are very accurate.

    Consulting the chart, you can see that there is NO pipe with a circumference of 8 inches!



    I suspect your method of measuring is inaccurate. (It can be hard to measure using a stiff metal tape) Try using a strip of paper approximately 1 inch wide and wrap it around the outside of the pipe. Where the end of the strip of paper meets the strip of paper make a mark. You can then use a straight ruler and measure the length of the paper from the end of the strip to the mark on the paper.



    As Kevin mentioned, there is a reducer bushing installed in the boiler port thread and since the boiler port thread fits 2 ½ inch pipe thread, that means the pipe attached to the bushing is less than 2 ½ inch pipe. (From the looks of it, It is 2 inch pipe)

    - Rod
  • jonny88
    jonny88 Member Posts: 1,139
    steamheads

    fail,,,if counted a few times he failed it,thats enough for me.fail is fail no guess work.call installer hopefully he will do right
  • BobC
    BobC Member Posts: 5,476
    Does he have the equipment

    There are some installers that simply don't have the equipment to thread anything larger than 2" pipe. In that case he would have to buy the cut and threaded pipe and nipples from a supplier (can take a few trips to the supplier) or rent a larger capacity threading machine for a day. That 2-1/2" pipe has to be for the entire header until it turns down to meet the equalizer.



    In any case that boiler should be piped per the installation manual, no if and's or buts. Use Rod's measurement technique and confirm that he did not use the 2.5" pipe and tell him it has to be redone in 2.5" pipe.



    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • you were right...

    I just measured the pipe using a piece of paper...and the results were 7.46 inches...effectively making the pipe in question...a 2" pipe as you all have thought...im slightly embarassed but was hopeful I didnt have to engage in a technical match with my installer...
  • BobC
    BobC Member Posts: 5,476
    No technical match

    The boiler HAS TO BE installed per the manual, the manual is very clear about the pipe sizes to be used. A properly installed boiler will work well and last a long time, if it's not done properly all bets are off - as is your warranty if anything goes wrong down the road.



    Hopefully you still owe him some money, if not I would not hesitate to tell him the next step is to call the manufacturer if he balks about doing it right.



    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • SWEI
    SWEI Member Posts: 7,356
    You could

    throw him a bone by offering to pay the difference in materials cost for upgrading the header from 2-1/2" to 3" pipe.
  • and the saga continues...

    So, I called Bryant and asked them about the risers...stating that the manual says it should be 2 1/2"...and if they could confirm that 2" was not correct...they told me to talk to another local installer...because there could be an 'allowable variance'

    SO, I called another Bryant Installation company, and they said they could not determine the issue without coming by and charging me for the diagnostics.

    I have no choice but to pay them for their 'Bryant' opinion.
  • Throw who a Bone?

    I apologize SWEI, but I don't quite understand.  Who am I throwing a bone to?  The original installer?  The 2nd Bryant vendor doing the diagnostics? 

    In addition, nobody ever mentioned 3'.  We were discussing 2" riser pipes that should be 2 1/2" risers.

    Please advise if 3" is a better option.
  • vaporvac
    vaporvac Member Posts: 1,520
    Technical support

    Another homeowner here...when you talked to Bryant did you talk to the Tech support people? These are the folks that help test these parameters and often write the spec manuals. Talk to them and go by what they say. Often the sales reps will not know the whys of the specs and may pass the buck.



    The 3" pipe is for the header; this is generally piped in at least one size bigger than the risers to allow space for the expanding steam, and for the condensate to separate out. This is a BEST practice and may not be suggested by Bryant so perhaps you could offer to pay the difference. Watch this great little video that clearly explains correct near boiler piping.

    http://www.heatinghelp.com/article/107/Steam-Heating/118/Steam-boiler-near-boiler-piping

    It's a shame we all have to become expert these days, but if you don't make the changes now, you'll be paying for the life of your boiler in gas bills and less comfort.
    Two-pipe Trane vaporvacuum system; 1466 edr
    Twinned, staged Slantfin TR50s piped into 4" header with Riello G400 burners; 240K lead, 200K lag Btus. Controlled by Taco Relay and Honeywell RTH6580WF
  • SWEI
    SWEI Member Posts: 7,356
    Bones

    2-1/2" is required for the risers and header.  The installer should be on the hook for the cost of remedying that.



    Increasing the size of the header to 3" is recommended.  You could offer to pay the additional cost for this.
  • Amazing

    You are all amazing! I was able to talk to both tech support people from Dunkirk and then from Bryant. They both supported your claim that the risers should be 2 1/2".



    I sent an email to my installer (owner) and he is going to send out a manager to take a look and make the necessary material list if necessary.
  • Rod
    Rod Posts: 2,067
    edited October 2013
    Good News!

    Great ! I'm glad you were able to get on the path to getting this resolved! Definitely a thumbs up for both Dunkirk and Bryant.

    - Rod
  • Jeff_44
    Jeff_44 Member Posts: 94
    Question Per Steamhead's commet

    I too have a boiler just like this - although it's labeled Dunkirk. I just noticed that the installer did the same thing and put a bushing on the return, reducing it from 2 1/2 to 1 1/2. We've had the boiler in place for seven years and have been happy with its performance. What is the effect of having the return piping reduced. I would like to make this right on my system. The installation manuel says that the return pipe should be 1 1/2 but when you look at the drawing there is not instruction for where the reduction from 2 1/2 to 1 1/2 should be.



    Thanks.
  • BobC
    BobC Member Posts: 5,476
    Should be ok

    As long as the boiler risers and header are full size (2-1/2") until it turns down to the return you should be all set. It makes little difference if the reduction takes place where the piping turns down or at the boiler return.



    If the boiler is working right you should be ok.



    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • and the saga continues...

    just got notice from the installer:



    ------------------

    I hope all is well. I have been in touched with Bryant in regard to the size of your header. The Bryant territorial manager said he is willing to stop by call and or give you a letter stating that the 2” header is the proper size for up to a 299,000 BTU boiler.



    If you want us to replace the header we will do it but in my 19 years I have never seen a residential boiler installed by us or any of our competitors in anything but 2 “.



    --------------

    Thoughts?
  • JStar
    JStar Member Posts: 2,752
    Thoughts

    How has he been in business that long? Yikes.



    Get the manufacturer out. Show the rep the installation manual. Have the rep sign a contract saying that the manul is WRONG in his opinion. Then you will be protected. I would not accept any of this lightly.
  • Manufacturer Evaluation - 1 employees viewpoint

    Manufacturer Evaluation - 1 employees viewpoint:

    One needs to understand that not all steam systems are the same and do vary from installation to installation that is why the term “recommended” is use and not “required” (in the manual)

    Your installer did use 2 – 2” risers along with swing fittings. I would have been concerned if he utilized 1 – 2” riser with no swing fittings. By utilizing the 2 – 2” he increased the steam volume over a single 2.5” OD riser, along with maintaining a consistent level within the boiler with the 2 risers. By having 2 risers along with the swing, which isn’t noted in the diagram, it provides a greater distance between the riser and take-off to the system to separate the water carried up with the steam producing dry steam. As previously noted your system take-off is after the 2 risers so there is consistent flow of any water carried up leading back through the equalizer and return leg piping.

    As I noted, the piping needs to be sized based on system as much as boiler. I do believe the current piping configuration would provide you of years of quality service though.
  • bullhead tee

    With the entire length of this post.. no one mentioned a major flaw before this installer did! There's a bullheaded tee on the main at top of the boiler.. that must be changed too!
  • bullhead tee

    With the entire length of this post.. no one mentioned a major flaw before this installer did! There's a bullheaded tee on the main at top of the boiler.. that must be changed too!
  • ChrisJ
    ChrisJ Member Posts: 15,583
    edited October 2013
    What?

    The first reply to the thread mentions it.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • JStar
    JStar Member Posts: 2,752
    Steam

    Rubbish. R-u-b-b-i-s-h.



    I would demand to talk to engineering, or find out exactly why the manual says one thing but tech support says another. Again, have them send a written and signed document stating that the manual is wrong.