Too much to list
gcp13
gcp13 Member Posts: 122
Not sure what they were thinking
I don't know where to start
2 in header?
Bullheaded tee,no swing joint
16 in. A Dimension
Level mains and back pitched drip returns
Main air vents 27" above waterline, above boiler
Plugged pigtail & 3/4 90 for presuretrol
Hartford loop close nipple 2 " above waterline
Auto feeder wired wrong not working
  • kevin_58
    kevin_58 Member Posts: 61
    boiler
    Looks like that boiler should be in a pit.
  • JStar
    JStar Member Posts: 2,752
    Steam
    This is why drop-headers were invented. But, then again, knuckleheads think a dropped header is just a way to get a bruised toe.
  • kevin_58
    drop header
    A drop header wouldnt work there, He said there is 16 in of a dimention. It needs to be in a pit or needs a condesate pump.
  • ChrisJ
    ChrisJ Member Posts: 15,708
    Header and pump
    In my opinion it needs a drop header and a condensate pump.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,846
    Hartford Loop?
    It looks like a completely dry return to me. Probably not a good idea with that A dimension. It probably calls for water mid-cycle, so add "fluctuating water line" to the list of troubles.
    I'm not sure how you measured that A dimension. Is that from the max water line to the header? If there's more than 28" from the water line to the main a drop header should work.
  • gcp13
    A dimension
    I measured A dimension from where the
    Feeder satisfies the lwco.
    At that point it was 2 in below Hartford loop
    Close nipple
    It was a toss up weather to raise up above
    Close nipple or get as much distance as possible.
    I would like to pipe the drip down into a wet return and then back to the boiler
    Customer doesn't want to do any work yet ???
  • nicholas bonham-carter
    Bad install
    What were the symptoms which led to the service call?--NBC
  • gcp13
    Check heat
    Check heat for the season
