Vent Damper Motor Jamming

Options
Jim Ward
Jim Ward Member Posts: 7
I have a Fieldcontrols flu vent damper that was installed three years ago along with my then-new boiler. Suddenly, it is jamming and preventing the boiler from starting. If I shut the power to the boiler off, and then on, it will work again. Just wondering if these commonly fail like this and if there is anything I can do other than replace the entire motor module?



Here is the specific part I am referring to - <a href="http://www.pexsupply.com/Field-Controls-46491600-Vent-Damper-Motor-Assembly-Plastic-Base">http://www.pexsupply.com/Field-Controls-46491600-Vent-Damper-Motor-Assembly-Plastic-Base</a>

Comments

  • Tim McElwain
    Tim McElwain Member Posts: 4,621
    Options
    Make sure it is

    positioned correctly on the flue pipe and not binding due to a poor fit. It is also from my many experiences with vent dampers better to relocate the damper as close to the chimney or vertical vent as possible as the high temps closer to the equipment affect its operation.
  • Steve Whitbeck
    Steve Whitbeck Member Posts: 669
    Options
    end switch

    The end switch is more than likely going bad. Usually takes 10 years.