BTU output for steam boiler

cdm
cdm Member Posts: 77
My radiators E.D.R.is 210 sq.ft. or requiring 50,400 BTUs of Boiler output.  The closest Weil McLean gas fired unit is 47,000 BTUs.  Would I be making a mistake getting a boiler that is 7% smaller than calculated or should I look for another vender to fit the 51,000 BTUs calculated.



thanks cd mulford

Comments

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,576
    edited January 2013
    Undersized-a bit

    If you go with that size, then make sure the main venting is super sized, and the radiator venting is more restrictive to get the steam into the mains first, and then rising up each riser simultaneously.

    You could check with the manufacturer if the burner could be up fired a tiny bit to compensate. I would like to hear others opinions on this.

    Insulation on the pipes would be a must with this.--NBC
  • Steamhead
    Steamhead Member Posts: 16,796
    edited January 2013
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • cdm
    cdm Member Posts: 77
    BTU output for steam boiler

    Thanks - I appreciate your input, and will talk to my contractor.



    cd mulford
  • cdm
    cdm Member Posts: 77
    BTU output for steam boiler

    Thanks for your input - I will check it out as another way to go.



    cd mulford