BTU output for steam boiler
cdm
Member Posts: 77
My radiators E.D.R.is 210 sq.ft. or requiring 50,400 BTUs of Boiler output. The closest Weil McLean gas fired unit is 47,000 BTUs. Would I be making a mistake getting a boiler that is 7% smaller than calculated or should I look for another vender to fit the 51,000 BTUs calculated.
thanks cd mulford
thanks cd mulford
Undersized-a bit
If you go with that size, then make sure the main venting is super sized, and the radiator venting is more restrictive to get the steam into the mains first, and then rising up each riser simultaneously.
You could check with the manufacturer if the burner could be up fired a tiny bit to compensate. I would like to hear others opinions on this.
Insulation on the pipes would be a must with this.--NBC0 -
Try a Peerless 63-03L
at 233 square feet:
http://www.heatinghelp.com/forum-thread/139406/Peerless-63-3L-Install-by-All-Steamed-Up-IncAll Steamed Up, Inc.
Consulting0 -
Thanks - I appreciate your input, and will talk to my contractor.
cd mulford0 -
Thanks for your input - I will check it out as another way to go.
cd mulford0