NTI Ti-150
Options
AFred
Member Posts: 81
in Gas Heating
Having trouble with a trinity Ti-150.
When I got there it would ignite and run for 3-12 seconds and dropout.
Ez, bad flame recification. I knew it needed to be cleaned so I tear it down and it was nasty. CLR it, scrub it, CLR it, scrub it..... I get it all back together and grab my anylizer. I fire it up, same problem flame drops out after 3-12 seconds. Check flame current at ignition module 3~4. Pull it, clean it. No change. So I order a new flame sensor. Get back few days later slap in the new flame sensor. And tada, same problem. Check flame signal at module and I'm getting a solid 7. Now I'm getting an error code an 'ER6' (flame lock-out). I am not getting the 3 flashes on the fenwal (module). I'm stuck, what do I test next? I ordered a new module, of corse they dont stock them here in the metro, I mean why would a wholesaler keep repair parts in stock on such an old boiler?(7years) Sorry, I'm getting whiney too.
Ideas anyone? Am I missing anything obvious?
-Andrew
When I got there it would ignite and run for 3-12 seconds and dropout.
Ez, bad flame recification. I knew it needed to be cleaned so I tear it down and it was nasty. CLR it, scrub it, CLR it, scrub it..... I get it all back together and grab my anylizer. I fire it up, same problem flame drops out after 3-12 seconds. Check flame current at ignition module 3~4. Pull it, clean it. No change. So I order a new flame sensor. Get back few days later slap in the new flame sensor. And tada, same problem. Check flame signal at module and I'm getting a solid 7. Now I'm getting an error code an 'ER6' (flame lock-out). I am not getting the 3 flashes on the fenwal (module). I'm stuck, what do I test next? I ordered a new module, of corse they dont stock them here in the metro, I mean why would a wholesaler keep repair parts in stock on such an old boiler?(7years) Sorry, I'm getting whiney too.
Ideas anyone? Am I missing anything obvious?
-Andrew
0
Comments
-
NTI
Contact NTI, they have a trouble shooter in all regions!0
This discussion has been closed.
Categories
- All Categories
- 85.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 424 Carbon Monoxide Awareness
- 73 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 129 Geothermal
- 160 Indoor-Air Quality
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 884 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 58 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements