retrofit over concrete

Our downstairs is concrete and we want to know the best product to install over the concrete without raising the floor too much.  House built in 70s and ceiling isn't too tall.  Downstairs consist of family/game room, 2 bedrooms and a bathroom.  Have hydronic system.  Should we install thermal panels or thermofin?  Do we put a moisture barrier down and then plywood or is there something else we can do.  Reading about these products and just confused.  

Comments

  • SWEI
    SWEI Member Posts: 7,356
    Is this slab on grade?

    If so, the lowest profile solution I have found is Roth Panel.
  • NRT_Rob
    NRT_Rob Member Posts: 1,013
    great product

    for that application. I second Roth Panel. not cheap, but it is a great choice if your slab is not insulated already.
    Rob Brown
    Designer for Rockport Mechanical
    in beautiful Rockport Maine.
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,853
    Roth panel on the ceiling works fantastic as well...

    And you could end up with less head space lost between the ceiling and floor.



    ME
    It's not so much a case of "You got what you paid for", as it is a matter of "You DIDN'T get what you DIDN'T pay for, and you're NOT going to get what you thought you were in the way of comfort". Borrowed from Heatboy.
  • lvremodel
    lvremodel Member Posts: 3
    retrofit over concrete

    Thanks, sounds good.  It may be insulated, but don't know for certain.  Did a test and no moisture, but it is concrete.  
  • lvremodel
    lvremodel Member Posts: 3
    retrofit over concrete

    Interesting idea, always heard heat rises, so won't we have to run at a higher temp to get the room warm?  We live in Montana.  We are planning on putting a sound deadening insulation.  
  • SWEI
    SWEI Member Posts: 7,356
    heat just moves towards cold

    Hot air and hot water both rise, since they have lower densities than their cold counterparts.



    Conduction is the issue inside the floor, and only R-value will do what you want.
  • NRT_Rob
    NRT_Rob Member Posts: 1,013
    radiant ceiling is great

    but not over uninsulated slabs.
    Rob Brown
    Designer for Rockport Mechanical
    in beautiful Rockport Maine.
  • ThatGuy
    ThatGuy Member Posts: 2
    Radiant walls?

    Saw this on a job side one time where they could not get enough heat out of the floor, so they added supplemental heat to a couple of exterior walls. They added QuikTrak on the lower part of you walls (less than 4'), unless you never plan on hanging pictures; shoudl not effect you ceilign heights
  • Dave H_2
    Dave H_2 Member Posts: 550
    Radiant Walls

    Is this basement a below grade basement? Without heat, does it maintain a decent temp all by itself (50-55F)?



    My point is, I did a build up of my basement floor and added radiant. However, the one thing that you want from a radiant floor system is warm floors. I don't experience the warm floors much, the heat load is so low that the floor doesn't stay on too long in order to satisfy the heat call.



    I have done a few radiant wall projects, but without panels. looped the tubing in the wall cavities and give it a couple of twists and staple to the sides of the studs so that the tubing crosses itself a few times. The tubing is "free-Flowing" so that any nails or screws put into the walls, the tubing will move out of the way.

    Insulate behind, and yes even install on inside walls for ease of install.



    Dave H.
    Dave H
  • Jean-David Beyer
    Jean-David Beyer Member Posts: 2,666
    I do not think it matters how long the heat is on.

    "However, the one thing that you want from a radiant floor system is warm

    floors. I don't experience the warm floors much, the heat load is so

    low that the floor doesn't stay on too long in order to satisfy the heat

    call."



    My house here in New Jersey (design temperature: 14F) has low heat load too. I have outdoor reset so the supply temperature can be quite low to the radiant slab floor. It can be on as long as 18 hours a day, but the floor temperatures are very low until it gets down to about design temperature. Then the floors can get up to 80F. They are only then warm enough to notice (although my IR thermometer notices sooner). And it is better when stepping out of the shower onto the marble tile floor than if it were unheated. But even then, I would usually not call it warm.



    I think this "warm floor" stuff is mostly advertizing hype. True, the floors are warmer than they would be if they were not heated.
  • Harvey Ramer
    Harvey Ramer Member Posts: 2,239
    Your floors can be as warm as you want them to be.

    All you have to do is loop zoning based on odr. Of course with proper loop placement.
  • Jean-David Beyer
    Jean-David Beyer Member Posts: 2,666
    Can you explain what you mean?

    If I make my floor any hotter than my present reset curve specifies, I will get terrible overshoot, and they will not remain hot very long, since the present low temperatures of the floor (low 70s) supply enough heat. If I could change the floor temperature rapidly (impossible: concrete slab at grade), it would probably be hot for only a few minutes.



    So how do you figure I could run that floor hotter without overheating the place? I would not wish to open the windows to increase the heat load.
  • Harvey Ramer
    Harvey Ramer Member Posts: 2,239
    I don't care what house you reside in

    There is a percentage of the floor where your feet normally reside and and a percent where your hardly ever trod. Take the former and zone it to be on all the time. Take the latter and zone it only to come on after the outdoor temp has dropped below a predetermined setpoint. It will require the heated area of your floor to run at a higher temp all the time.



    Like i said before, If you want to do that loop placement is critical.
  • Gordy
    Gordy Member Posts: 9,546
    edited August 2012
    Radiant floor temps

    Radiant floors should feel neutral IF the dwelling has a decent envelope, and the system has proper controls. The only time you will notice a warm floor is when outside temps are extremely low for extended periods. Or iif the envelope is like a submarine with screen doors.



    For the most part a basement is low load once the rfh has reached equilibrium.



    Edit: Harvey does have a solution IF the warm floor sensation is desirable. Concentrate tubing in pathways traveled most of the time. Creating two zones with loops in non foot traffic areas.



    The only problem is future movement of furniture. That's why I like the radiant ceilings. Save the floors for baths, and kitchens.





    Gordy
  • Jean-David Beyer
    Jean-David Beyer Member Posts: 2,666
    OK: I will do that...

    next time I replace the slab under my house. I will even make sure it is insulated underneath and around the edges.
  • Dave H_2
    Dave H_2 Member Posts: 550
    Basement Warm Floor

    Yes, I could make my floors run "warm" all the time but that would have required making the boiler room more complicated. Design water temp was 104 while the rest of the house was 130 on a design day here on Long Island.

    I did mixing reset, so that brought the water temps "closer" together and there are separate zones.

    I could have added another mix, another circ.....I should have been clearer. Also adding the radiant floor to an existing basement added alot more cost compared to doing a radiant wall. Quik-Trak, added on top of a basement subfloor system, Dri-Core.



    Dave H.
    Dave H