radiator issues

Options
srock
srock Member Posts: 1
i am working on a church and i have a two pipe steam system. I cannot get any heat to some of the radiator the main line is hot and some of the take off lines are hot. I can remove the valve and i get no steam at the radiator there is not even pressure there it is like the pipe is not even connected.all the traps have been rebuilt and the return line screens have been cleaned.any suggestions would be appreciated.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,323
    Options
    The first thing that comes to mind

    is to check the pitch and routing of the runouts connected to the problem radiators.  If there is a way for condensate to get really trapped, you could wind up with no pressure and no steam.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Paul48
    Paul48 Member Posts: 4,469
    Options
    Physically

    removing the valve, or disconnecting the union?
This discussion has been closed.