Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Installing outdoor reset thermistor in air intake

Options
TonyS
TonyS Member Posts: 849
I have installed these on April air humidifiers but was wondering if anyone has done this on a boiler? Sometimes it can be a pain finding an area out of the sun.. any pros or cons to doing this?

Comments

  • HDE
    HDE Member Posts: 225
    Options
    Not good

    Not advisable

    Humidifiers only work after the furnace is operating thus outdoor air is drawn across the sensor.



    If the sensor for ODR is in the pipe located in a conditioned space it won't read proper temp and likely stay in warm weather shutdown.
  • JohnNY
    JohnNY Member Posts: 3,230
    edited October 2011
    Options
    You mean the makeup air into the room?

    I do it all the time providing there's a constant inward flow of air.



    It's not ideal, but in attached NYC townhouses and multi-family buildings, often there is simply no better place to put the sensor.



    The outdoor air reading may be off by off 2 degrees or so, but it'll work fine. I promise.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • HDE
    HDE Member Posts: 225
    Options
    ?

    I'm positive he's asking about installing it in the boiler PVC intake pipe, knowing aprilaires instructions



    If boiler hasn't run it won't sample outside air
  • TonyS
    TonyS Member Posts: 849
    Options
    I am talking about the PVC intake

    But I dont need to activate the warm weather shutdown and I could set minimum water temp above 75. I believe the resistor on the TT is 10k and can probable be replaced with the aprilair unit.. The aprilaire unit is designed to fit into a small hole drilled into the air intake and a clip to hold it.  I will check the k value and if it is compatible I will try it on my TT in the shop. I will let you know what my results are.
  • JohnNY
    JohnNY Member Posts: 3,230
    Options
    Oh!

    No. You can't do that. You,d need a constant draw from outside or it won't work. 1
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • TonyS
    TonyS Member Posts: 849
    Options
    Im thinking that

    if the thermistor is in the pvc and the unit is idle, the controller would reset the temp to whatever temp it is in the pvc,down to my minimum water temp setting. But as soon as there is a call for heat and the tt terminals close, the inducer would start and cool the thermistor before the ignition stage even fires. By the time the boiler starts to produce heat the outdoor reset should be stabilized. Maybe I am missing something here but it seems as though it should work fine. What problems do you think could arise? The warm weather shutdown was something I didnt think about but most single family dwellings I wont use that. I let the customer decide when they want heat. Even if they want heat just to a towel warmer or to take the chill off tile on a warm day. I am just looking for options because some of these large semi city homes I dont have access to a north wall and the last one I did I must have spent 3 hours getting that outdoor stat to a suitable location.
  • heatman101
    heatman101 Member Posts: 19
    Options
    Never thought of that...

    however, I think you will find that the sensor will not react quickly enough...and the boiler may cycle off before it cools the sensor to the correct temperature.

    It really would not be hard to experiment a try it...bet you will find that it really don't work so hot though...



    But hey... if it does work, let up know...
  • JohnNY
    JohnNY Member Posts: 3,230
    Options
    I don't like to answer questions with an opinion...

    ...but I do think the rapid changes in temperature between the boiler being idle and still connected to the heat exchanger and the drop from the incoming air will do nothing good for the reset curve.



    That said, I'd love for you to try it and let us know how it went.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,853
    Options
    I don't know....

    Depending upon who's boiler, it cold create more problems than what its worth. When the boiler shuts down the burner, residual heat could rise up back through the combustion air pipe, causing the logic to go off on WWSD. Until all residual heat is dissipated, you could be locked out by the fickle finger of fate.



    I have used the C/A pipe as a chase to get the sensor located outside...





    ME
    It's not so much a case of "You got what you paid for", as it is a matter of "You DIDN'T get what you DIDN'T pay for, and you're NOT going to get what you thought you were in the way of comfort". Borrowed from Heatboy.
  • Ironman
    Ironman Member Posts: 7,376
    Options
    This One Definitely...

    Deserves the definitive hydronic answer: "it depends".



    If the c/a pipe is a long horizontal run with a goose-neck, or if it connects directly to the gas valve, and if the sensor is placed in the outdoor portion out of the sun, then maybe it could work. Otherwise, I'm skeptical too. But, I am curious.



    Give it a try and let us know.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • gennady
    gennady Member Posts: 839
    Options
    outdoor sensor

    I was thinking about it , but never done it. I think, if sensor is installed right in the inlet fresh air elbow, it might work, is it will be in the shadow and read actual outdoor air temperature without influence of sun, walls, windows and others sources of heat..  
  • TonyS
    TonyS Member Posts: 849
    Options
    8 days without electric

    Sorry I didnt get back to this thread. I lost electric 8 days ago in that freak storm and I was last on the list to get turned back on. I will try installing the thermistor as soon as I get caught up and share my results.

    I learned alot about generators in the last few day though.