MPO 84 replacing oversized V8 has a higher cold return

Options
I'm replacing an oversized warn out Burnham V8 with an MPO 84.  On the plmbing side most everything seems the same, but the cold return is at the top of the MPO.  All my circulators are slightly lower on the return than the actual return port on the MPO boiler and they are all connected to a 1 1/2" at floor leval where the old V8 returned.   I'm wondering if I need to move all three circulators up above the return port height on the MPO or if I can just take the 1 1/2" return pipe up to the return port on the MPO boiler?

 

On the smoke side, does the flue pipe inside (boiler to chimney) have to be SS or is galvinized OK?  And if SS, which type, 316 or 304?

Comments

  • JStar
    JStar Member Posts: 2,752
    Options
    RE

    You should be moving the circulators to the supply side of the system, anyway.



    Otherwise, rerouting a return pipe is not a big deal.
  • lchmb
    lchmb Member Posts: 2,997
    Options
    vent pipe

    can be galvanized unless local code requires something different...