Hissing and Gurgling
TeachMeSteam
Member Posts: 128
I recently replaced a main vent, hoping to get rid of the hissing and gurgling coming from the radiator valves. However, the radiator valve is still hissing and gurgling.
Can you guys suggest a solution?
hissing&gurgling
what size main vent did you put on?
what is your main pressure-hopefully less than 2 psi ?--nbc0 -
Size
The main vent I put on was a Gorton #1. The radiator valves are various. Most are maid o mists. one of them are a gorton #6. but the ones on the 2nd floor all hiss and gurgle.
the psi is set to about 1.5 via the pressutrol. it's hard to tell what it actually goes up to since the pressure gauge has a range of 0-30 psi. This gauge doesn't move at all by the time the boiler cycles out. (I wonder why they installed a high pressure gauge when a small one would have been more appropriate. oh well.)0 -
useless 0-30 pressure gauge
why indeed do the manufacturers, and installers not install a good low-pressure gauge on every steam boiler sold? and yet, the owner will never know if the pressuretrol is working properly, unless one is installed! without an accurate reading, the owner, will also not know either whether main venting is adequate [back-pressure during venting], or how much extra fuel is being burned to maintain a higher than normal pressure [8 ounces].
after all would you check your tires with a 5000 psi hydraulic gauge?--nbc0 -
gurgling, hissing
To me gurgling suggests that a liquid (condensate) is trying to go down, but runs into a restriction which causes it to dam. Once the height of the liquid gets to a certain level, the weight of itself, forces it down. Once it finds a way to go down, the air is allowed to come up. The air coming up is making the gurgling sound. The first thing to check is to make sure the radiator valves are all the way open. Secondly, make sure the radiators are pitched. Not too much, just enough that the condensate will flow. If these 2 suggestions don't help you might have to make sure the runouts and mains are pitched properly.
Hissing is a sign that the pressure is too high. Mine start hissing at about 1psi. Install an additional gauge. The gaugestore.com sells a Wika 0-3psi. Post a photo of your existing pressuretrol/gauge setup and someone will advise you how to add an additional gauge.0 -
Thoughts
A single Gorton #1 may not be adequate, but inadequate mains venting is probably not the cause of the hissing and gurgling. When radiator valves are not fully open the stem and disk are in the path of the steam flow and will create condensate that pools and gurgles inside the valve. The fact that it is only the upstairs radiators is a clue that maybe the upstairs gets too warm, a common defect, and people are trying to regulate by manipulating the valves.0 -
What can I do?
Thanks for sharing your sentiment. I thought I was being a little crazy to think that they didn't do it right.
This was for a recently installed boiler by a reputable company. They also installed a pressuretrol in which you can't lower the PSI less than 1.5 PSI which is a little frustrating since this is for a very small home.0 -
Do you think i should replace the valves?
This is for a new boiler. and I replaced the valves with gorton's and maid o mists. so it's probably not that the valves are faulty.
i'm not sure how to tilt the radiators since these are recessed radiators that are within the walls. is it possible to tilt these types of radiators?0 -
Misunderstood
When you wrote valves I thought you were referring to the radiator shut-off valves, not the air vents. Since it's a new boiler the culprit is probably wet steam. The boiler probably needs to be skimmed. Post a picture of the piping around and above the boiler.0 -
main and runout pitch
1 of the 2 mains has water hammer but not sure how I would go about creating a pitch for that. also, is it possible to radiators that are recessed within the wall?
I'm going to try to get the pressuretrol and gauge replaced with a vaporstat and low pressure gauge...0 -
Air vent and Supply valve
Here is an explanation of terminology. When I was suggesting that you make sure the valve is open, I meant the supply valve. There is likely nothing wrong with the air vent, as you said they are new. I am not sure how to pitch that kind of radiator, I thought you had the cast iron type. Please see the enclosed photo. Is it possible for you to post some photo's of what we are working on?0 -
Pictures
Here are pictures of the setup.
(Sorry for the pictures being sideways but I can't figure out how to put them upright.)0 -
Gurgling
I have never seen that type of radiator. But if it were mine, and I wanted to check the pitch, or tilt as you say, I would put the level right where I drew the red rectangle. After you look with the level, tell us which side is higher. The air vent side or the supply valve side.
Make sure the supply valve is open all the way. Counterclockwise opens it.0 -
0-3 pressure gauge
Here is a photo of one way to add a 0-3 psi gauge. You must leave the 0-30 psi installed for insurance reasons.0 -
Because
it costs extra.All Steamed Up, Inc.
Consulting0 -
1920s convector style
Most of my rads are the same, you should be able to lift those to shim if need be, but they do weigh a ton! Mine just sit on the four feet, there isn't any provisions on it anywhere to be bolted or secured to anything. When heating well, you should feel a warm breeze rolling off of those!steam newbie0 -
Exactly
It doesn't look bolted down and it does sit on 4 legs but my weak muscles do not seem to make the radiator budge at all.
Do you think using a car jack would be ok?0 -
Did you
check the radiators with a level yet? Which way is it sloped?0 -
It's level
I checked with a level and all the radiators are pretty much level. So, that's a bad things. I tried lifting. I huffed and puffed but to no avail. It might be that the legs are painted to the floors.
I was thinking of using a car jack. Is that crazy?0 -
Curious to what your settings are
I can't tell by your pictures but what are your cut in and cut out's?
Also, what kind of vaporstat do you have?0 -
Level is not so bad
The radiator only needs to be the thickness of a couple quarters, higher at the air vent end. The gurgling might be in the supply valve, have you made sure its all the way open? Car jack is not a good idea. You might crack the radiator, then you will have a bigger mess to fix. They dont make them anymore. If you break it how will you find a replacement. If the radiator is painted to the floor, and it has to be lifted, get some paint stripper and a putty knife. Free it from the floor before you try to lift it.0 -
That vaporstat is not mine
I used that photo because it was closer to your type of setup. I have a L408J-1009. Mine will allow the burner to come on at anything lower than 3oz. It will shut off the burner at 8oz. The settings to acheive that are Main 8oz and Diff 5oz. Don't just run out and buy a vaporstat, just add a low pressure gauge for now. Maybe your pressuretrol can be adjusted to reduce your pressure. What is the model number of your pressuretrol?0 -
Honeywell L404F1060
The pressuretrol's cut off can't go below 1.5 psi. if I try to set it lower, the boiler will not cut in. It just stays off. I guess when I moved it below 1.5 psi, the pressuretrol just assumes I set the cut off to 0.
I have a 900 sq ft home and longest run to the radiators is at most 100 ft. i guess that means 2 oz of pressure differential is all i need. so maybe I need a vaporstat?
I'll post a new thread with a question I have on vaporstats. this thread is getting a little long.0 -
Dont forget
to post your pictures again in the new vaporstat post.0 -
Settings
That's a picture of my setup and it is currently set for a 12 oz cut out and a 4 oz cut in.
I also have a small house, the EDR (sq footage of all the radiators) is about 190 sq ft. I do have some short cycling issues because the 15 yr old boiler is over sized but the system is otherwise efficient and relatively quiet.
3PSI gauge0 -
my .02
The gurgling might be in part caused from the actual radiator vent. I purchased the same valves from the local HD and had nothing but problems with them. There is no fine adjustment on the valve, so you have to change the size of the screw-in vent. I also noticed that since these valves don't have a tongue that drains the condensate back into the radiator that if there is over condensing going on, it builds up in the valve causing the radiator to gurgle and spit and sometimes become blocked. I removed all the those vents and replaced them with high quality vents. Some Gordon's and some vari valves (that I closed all the way to slow the venting.. They still vent very fast when closed all the way).
I also replaced the actual valve on the radiator. It's hard to tell from your picture, but there this a difference between a hot water valve and steam valve. The steam valves have a bulbous body that gives more room for steam and water to pass. I had a radiator that Swooshed and Gurgled. By changing the vent and the valve, it is now perfectly quite.0 -
Pressuretrol differential setting
Earlier in this thread you mentioned that you can't set the pressure limit lower than 1.5 PSI because the boiler will not cut back in. Looking at the photos, the differential appears to be set higher than the cutout pressure, which is probably why the boiler is not coming back on when the cutout is set less than 1.5 PSI. The differential subtracts from the cutout setting, so if the differential is higher than the cutout, you will need negative pressure (vacuum) for the boiler to cut in again.
Try setting the differential to less than 1PSI or so and then reset the cutout lower again and see what happens0