Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

ITT Nesbitt ptact

keith_27
keith_27 Member Posts: 64
Looked at a nesbitt  n15-58  wall heater today.   The fan motor is faulty.   After checking the unit  how would i acess the motor and wheels ?

Comments

  • Tim McElwain
    Tim McElwain Member Posts: 4,612
    I am not familiar with

    that unit but most wall furnaces have the blower in the top of the unit and it blows down over the heat exchanger. Some pictures would help.
  • Wayne_16
    Wayne_16 Member Posts: 130
    Most wall furnaces

    On most wall furnaces, the blower assembly is easily removed with a couiple of screws and disconnecting the wires or plug. Fan, shroud and wheel or blade as an assembly.



    Minnesota Wayne
  • GD
    GD Member Posts: 2
    NESBITT

    I supply all NESBITT OEM parts.  Let me look into this and see if I can find some O&M literature for you.



    If you need parts shoot me an e-mail.
  • GD
    GD Member Posts: 2
    NESBITT

    I supply all NESBITT OEM parts.  Let me look into this and see if I can find some O&M literature for you.



    If you need parts shoot me an e-mail.
This discussion has been closed.