Is the HB Smith 8 Series any good?

osb
osb Member Posts: 1
I recently got a quote from a contractor to replace my old boiler. He recommended the HB Smith 8 Series. Does anyone know if this model is any good?

Comments

  • kcopp
    kcopp Member Posts: 4,419
    I have used....

    Smith 8 series boiler for years... both in steam and hot water applications. I have never had an issue and if there were any I know the factory rep. will be right there.

    I especially like it for steam. kpc
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,540
    If you

    If you want a single pass boiler,they're fine!
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • Steamhead
    Steamhead Member Posts: 16,796
    Do you have

    a steam or hot-water system?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,318
    I like them.

    The boiler is seldom the issue with an installation. Like Cezar says " It is seldom the dog , but the owner that is the issue." The boilers can be great and the install is bad, Today I saw a mega Steam by burnham installed by a competitor that had no main vents. It also had the dry returns tied together then dropped to the return at the hartford loop. They also used an iron circulator to the indirect heater with no bypass for temperature control of the water going through the circulator. also no provision was made to flush the wye strainer, that I was shocked to see they remembered. The new boiler is not saving the homeowner much on their oil bill compared to their old 1970's boiler. If you can not tell seeing good boilers installed poorly gets me steamed, in a bad way.
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,318
    I like them.

    The boiler is seldom the issue with an installation. Like Cezar says " It is seldom the dog , but the owner that is the issue." The boilers can be great and the install is bad, Today I saw a mega Steam by burnham installed by a competitor that had no main vents. It also had the dry returns tied together then dropped to the return at the hartford loop. They also used an iron circulator to the indirect heater with no bypass for temperature control of the water going through the circulator. also no provision was made to flush the wye strainer, that I was shocked to see they remembered. The new boiler is not saving the homeowner much on their oil bill compared to their old 1970's boiler. If you can not tell seeing good boilers installed poorly gets me steamed, in a bad way.
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
This discussion has been closed.